Inducer Motor Will Not Start - HVAC - DIY Chatroom Home Improvement Forum
Old 01-12-2012, 07:30 PM   #1
inducer motor will not start
I have a ducane furnace with a honeywell board. The hvac repair guy said the board was bad, so I put in a new one with the same result. If i supply power to the inducer motor I can get the furnace to run. Then turn the thermostat off and is shuts down. Thermostat back on and nothing happens until i jump in some power to the inducer fan.
mwick9 is offline   Reply With Quote
Old 01-12-2012, 07:37 PM   #2
An old Tradesmen
Rewards Points: 7,328
Could be an open roll out switch.
Old 01-12-2012, 11:40 PM   #3
how
Rewards Points: 1,104
Do you have a flashing diagnostic led on the board that is giving you a code for what is wrong in the furnace? If its behind a door with a kill switch, tape the switch shut so you can open the door after the next lockout without shutting off the diagnostic led code.
how is offline   Reply With Quote
Old 01-13-2012, 06:40 AM   #4
HVAC Tech/ Browns Fan
Is that a Smartvalve?
Tator1076 is offline   Reply With Quote
Old 01-13-2012, 07:57 AM   #5
role out switch is fine
There are two role out switches and a pressure switch on one circuit. Both role outs are closed and the pressure switch is open at the start of sequence. Once I make the inducer fan come on, the pressure switch closes, completing this circuit and allowing the burner to fire up.
I am not sure what is meant by the smart switch. Is the part of the gas valve? How would I troubleshoot it? Can it control the inducer fan being turned on?
If the thermostat is closed. When plug in the furnace, the control board gives 3 quick blinks, then goes to a constant bright heartbeat.
If the thermostat is open, it goes straight to the bright heartbeat. When I close the thermostat at this point, the heartbeat does not change, but I hear a click in the furnace.
To get the furnace to come on, I have moved one of the wires on the control board from the blower that should on an "UNUSED" pin the the "HUM" pin that seems to be tied to the "IND" pin. Then I pull the wire off of the limit control sensor, indicating overheating. This turns on the blower motor and now the inducer motor will come on. Replacing the wire on the limit switch make the furnace happy and allows the gas to come on and the furnace to fire up.
Old 01-13-2012, 08:21 AM   #6
Wouldn't be the first time in history that a part was bad right out of the box. Double check that everything is wired correctly and there are no loose connections. If that's all good then it sounds like you got a defective board.
Old 01-13-2012, 11:38 AM   #7
smart valve
Does anyone know if a smart valve issue could prevent the inducer fan from starting?
Old 01-13-2012, 12:42 PM   #8
If you have a smart valve that has a blue head, chances are the inducer is wired to it and the vale could be intermittent. Again, assuming yours is wired this way.
hvac5646 is offline   Reply With Quote
Old 01-13-2012, 08:38 PM   #9
Rewards Points: 582
picture of furnace with door off would help...
Old 01-15-2012, 07:52 AM   #10
attached is the wiring diagram for my furnace
Does the EFT on the SV9501 smartvalve control turning on the inducer?
Old 01-15-2012, 08:05 AM   #11
This is a 24v smart valve system. The inducer is activated from the control board. The valve is activated separately.
Old 01-15-2012, 02:42 PM   #12
put in old control board, works fine now
I put the old control board back in and everything works. I'll give the hvac guy who diagnosed that the control board was bad and assume it may be intermittent and that the new board was doa.
Thanks for all your help!!
Draft Inducer Squealing Noise rbh123456789 HVAC 9 01-05-2012 12:37 PM
American Standard intermittent inducer problem with presssure switch warning no such user HVAC 5 12-26-2011 05:20 PM
Inducer motor had been squeaking OhDamn HVAC 5 12-17-2009 09:19 PM
inducer fan runs constantly tibsmandu HVAC 3 11-29-2009 11:12 AM