Inducer and Ignitor starts but no gas
I am having a problem with my heating unit. The board is GMP100-3. When I turn on the heating unit, the inducer motor starts, ignitor glows and then nothing happens. The gas will not flow in to start and ignitor turns off and whole thing stops. This repeats for 3 times and then systems shuts down. I do hear few clicks during this cycle. What can possibly be the problem? Can anyone help??
hansim4 is offline   Reply With Quote
Old 03-15-2009, 02:15 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
What is the flash code on the control board?
Once you find it find the code chart and post the results.
Is this a 80 or 90+ % furnace?
Old 03-15-2009, 02:30 PM   #3
Rewards Points: 30
It gives one blink which means problem with gas flow, gas pressure, gas valve or flame sensor. I did clean flame sensor with sand papers but didn't make any difference...
I am not sure what 80 or 90+% means. Can I look up this some where?
Old 03-15-2009, 02:34 PM   #4
HVAC / Plumbing
do you have the means to check voltage at the gas valve ?? 80% 90% is the efficienty of the furnace
kenmac is offline   Reply With Quote
Old 03-15-2009, 02:36 PM   #5
Rewards Points: 560
Is the flue pipe metal or plastic?
Is this Natural gas or propane?
Old 03-15-2009, 02:38 PM   #6
Rewards Points: 30
It's natural gas for sure. What is flue pipe?
I asked my friend to bring a voltage meter so I can check this. Once I have the voltage meter, what should I do with it? What should be the correct voltage? If it's not correct, then how can I fix it?
Sorry for asking so many questions and thanks for everyone's help in advance.
Old 03-15-2009, 02:43 PM   #7
HVAC / Plumbing
The flue pipe is connected to the vent motor. You should have around 24 ac volts at the gv b-4 it opens
Old 03-15-2009, 02:43 PM   #8
Rewards Points: 560
Bare with me..look at the gas valve and tell me how many wires are going to it and if you can the terminal lettering.
What you need to do basically is take the black lead to ground and the red lead to each of the terminals to see if voltage is getting to the valve and though the valve windings.
The voltage is approx 24-27 vac
Old 03-15-2009, 02:56 PM   #9
Rewards Points: 30
There are 2 wires connected to gas valve. One is purple wire hooked to slot with V and P letters on the left side and 1 and 3 numbers on the right. The other wire is blue and is hooked to slot with letter C on left and number 2 on right..
BTW, my flue pipe is metal.
Old 03-15-2009, 03:11 PM   #10
Rewards Points: 560
Ok
Take the black lead and go to ground..Anything metal on the furnace
Take the red lead and go to the V terminal. Set the meter to AC voltage so that it will read 0-100
Have your buddy turn up the stat and make a call for heat.
On the first try for ignition measure the V terminal - Purple wire
On the second try for ignition measure the C terminal - Blue wire
Post results
If you have power on both terminals then you have a bad gas valve
If you have power on the purple wire but not on the blue wire. Then you will want to remove both wires and measure in ohms between the two terminals for continuity. If there is no continuity then you have a bad valve. If you have no power to the valve you may have a bad control board.
Old 03-15-2009, 03:43 PM   #11
Rewards Points: 560
Sorry, I got typing to fast.
If you have voltage in and out of the valve then you need to check gas pressure to the valve before replacing the valve.
Old 03-15-2009, 04:23 PM   #12
Rewards Points: 30
I found the problem. The purple wire had connector on top cover of the burner. It had no voltage. However, it also had a reset button. When I pressed the reset button and check the voltage again, it worked. I turned the unit on and everything works fine.
Thanks so much for your help. It's nice to know that there are people like you who will help others.
Take care and keep up the good work!!!
Old 03-15-2009, 04:26 PM   #13
Rewards Points: 560
Was this button you pressed on a disc type devise?
This could be a roll out limit switch and may be indicating that you have another problem.
Old 03-15-2009, 04:34 PM   #14
Rewards Points: 30
The purple wire from gas valve goes to side cover of the unit first. From there, it goes to top cover of the unit and then to the board. On top of the cover, it has a small unit with tiny rectangular button on top and 2 flat metal pieces on the side. The purple wires are connected to these 2 small flat metal pieces by sliding them into the metal, similar to way we connect USB devices to USB ports in computer.
How do I find out if there are other problems?? Is there any other tests I can do to check?
Old 03-15-2009, 05:04 PM   #15
Rewards Points: 30
I googled flame rollout switch and you are right, it is flame rollout switch that I pressed. The unit is working fine right now but should I be concerned here?