Inducer Fan Runs Constantly - HVAC - DIY Chatroom Home Improvement Forum
Old 11-29-2009, 10:31 AM   #1
inducer fan runs constantly
thanks for taking the time to read the post.
this is a trane xr90 gas furnace. the inducer fan runs constantly. the unit will run and meet the set point on the thermostat and then shut down except for the inducer fan running. the unit will not start again unless i manually reset the pressure switch - gently move air in the tube to the pressure switch.
i called for service and at that time it was an intermittent thing and the tech could not pinpoint the problem. since the service call i have identified the above sequence to get the equipment to start.
in addition to the service call i had the pressure switch changed and checked to make sure all condensation lines are clear.
any ideas as to what is causing this unit not to operate correctly?
thanks
tibsmandu is offline   Reply With Quote
Old 11-29-2009, 10:46 AM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 396
The circuit board is faulty. The relay for the fan is sticking. Sucking on the pressure switch damages it and it should be replaced also.
Old 11-29-2009, 11:08 AM   #3
if the fan runs will this cause the pressure switch fault?
Old 11-29-2009, 11:12 AM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 396
Yep. The board needs to see an open switch/circuit B4 it will work for the next cycle.
Blower fan runs constantly epowerfan HVAC 65 12-06-2011 06:57 AM
Trane Carrier XL80 fan runs constantly when switch is on jheavner HVAC 13 10-25-2008 09:54 PM
No flow to shower head; toilet runs constantly kathleentsy Plumbing 7 05-17-2007 09:05 AM
Bryant Inducer Fan Runs Constantly biglittledan HVAC 4 11-24-2006 11:23 AM