Old 09-09-2011, 07:34 PM   #1
inducer blower motor stays on 24/7
I'm troubleshooting an 80% furnace with an IFC board and its inducer blower motor stays on constantly even though the thermostat is set on Off and the fan on AUTO. Any suggestions anyone
alex1oo7 is offline   Reply With Quote
Old 09-09-2011, 07:47 PM   #2
30 year tech
hvac122's Avatar
Check the limits
hvac122 is offline   Reply With Quote
Old 09-09-2011, 08:51 PM   #3
biggles's Avatar
relay board contacts might be arck together remove the W wire off the board that is your heating call see if the relay drops the ID out
Old 09-10-2011, 02:50 PM   #4
REP
All of the above plus there is a relay that sends power to that motor.It is probably on that board.The contacts have welded themselves together.You might get that to release by tapping the handle end of a screwdriver on that relay ,but even if that works you need another board.
REP is offline   Reply With Quote
Old 09-10-2011, 04:05 PM   #5
biggles's Avatar
four calls come out of or OFF the board..the ID,pilot ignition, and the gas valve voltage then the supply fan motor on a timed delay the black cubed relays are the 115V loads..when your stat calls for heat the first thing to run is the ID
Tags
inducer motor , troubleshooting
Bryant Plus 90 - No Blower Ducaticorse HVAC 13 01-03-2015 04:39 PM
Draft Inducer Blower Not Blowing- LED Blinking 3 Times rust101 HVAC 10 04-09-2013 08:44 PM
Fasco blower inducer 7062-3136 Aziza007 Appliances 1 12-10-2010 07:40 AM
Replacement impeller and clip for Heil exhaust inducer blower iixeb HVAC 2 01-09-2009 08:36 PM
Replacement Inducer Blower caseywa HVAC 18 11-27-2006 03:42 PM