Old 02-18-2013, 09:38 PM   #1
I have an american standard freedom 80. The first burner is allowing flames to leak out of the back of the burner which triggers the open high heat device. What is causing this?
DaveM1. is offline   Reply With Quote
Old 02-18-2013, 09:39 PM   #2
Can I fix this myself?
Old 02-18-2013, 10:39 PM   #3
how
Pictures would help.
If this happens before the main blower comes on then...
you are probably talking about the gas backing out of the venturi opening of the burner because of a dirt/scale/rust obstructed burner diffuser.
Turn off the furnace power, remove the burners and wash them out.
how is offline   Reply With Quote
Old 02-18-2013, 11:05 PM   #4
REP
It sounds like you need a clean and check real bad.With that a gas pressure check and a draft check should be done.Ignoring this could lead to real bad medical problems.
REP is offline   Reply With Quote
The Following User Says Thank You to REP For This Useful Post:
hvactech126 (02-19-2013)
Old 02-19-2013, 06:14 AM   #5
An old Tradesmen
Does this happen as soon as the burners ignite, or only after the blower starts. if only after the blower starts. good chance you have a bad heat exchanger.
American Standard Freedom 90-No Heat pbrjtr1 HVAC 2 02-04-2011 11:28 AM