Hydronic Boiler Bang? - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-22-2010, 06:35 PM   #16
here is a picture of the valves cap on and cap off--are they spring type?
hydronic boiler bang?-dscf5119.jpg   hydronic boiler bang?-dscf5118.jpg   hydronic boiler bang?-dscf5117.jpg
matt teo is offline   Reply With Quote
Old 12-22-2010, 06:49 PM   #17
Experienced
Jackofall1's Avatar
Well there is good news and bad news at least the way it should have been done in the first place.
You did install the pump correctly for the system you have, the problem I see is the pump should be on the other side down stream of the expansion tank.
Not that it won't work the way you have it, it just won't work as well.
If you power up the (3) solenoid valves (zone valves) in the picture with an external source (if they are normally closed valves) and run the system you will avoid the water hammer (this is just a diagnostic suggestion). Caution valve are probably 12Volts (door bell transformer)
If that is the problem, then you can either
1 - move the pump
2 -change out solenoid valves for asco slow closing valves
3 - develop a "delay off" circuit for the solenoid valves.
See Attached
Old 12-22-2010, 07:06 PM   #18
Thanks again for the reply. I heard that the pump should be on the other side. So why did the valves suddenly create a water hammer effect? The system worked fine with the exact same set up last winter and this winter before I changed the circulation pump. I trust you, I'm just don't understand why I can't make it work now if it worked with this setup before. Any thoughts?
Old 12-22-2010, 08:15 PM   #19
Experienced
Jackofall1's Avatar
Chances are the pump you replaced was not developing the pressure and flow that you are now getting with the new one. With the increased flow the problems would be magnified.
A delay circuit would not be that hard to do and it would certainly take care of the problem.
I am wondering what the previous owner had to do to stop the pressure relief valve on the boiler from releasing as you are definately on the pressure side of the pump.
Need help fast please re hydronic boiler water supply and backflow DanDaMan Plumbing 21 12-22-2010 08:01 PM
Need help fast please re hydronic boiler water supply and backflow DanDaMan HVAC 6 12-11-2010 03:26 PM
I Need a New Boiler. What do i need to know New Boiler Co Plumbing 0 10-23-2010 07:03 PM
Hydronic boiler pressure question. RickInMissouri HVAC 1 01-23-2010 05:57 AM
Boiler w. Hydronic Air & Honeywell Aquastat DanA28 HVAC 1 01-08-2009 05:21 PM