HW Baseboard Gurgling - HVAC - DIY Chatroom Home Improvement Forum
Old 02-16-2009, 11:07 PM   #1
HW Baseboard gurgling
Air is constantly in the 2nd floor of my HW Baseboard system (2 zone, 2 pumps) even after I purge it out. The boiler is on the discharge side of the pumps, with the diaphram expansion tank and fill at the boiler high pressure releif valve. Boiler manufacture (weil mclane) recommended to repipe system to have boiler on suction side of pumps and move expansion tank & fill as well. I also heard from a contractor that the individual bleeder valves on each slant fin unit may fail and eventually leak air into system. I checked the bleeder valves, no water leaks observed. Is it possible for bleeder valves to leak air in although no water leakage is observed?
rcassidy is offline   Reply With Quote
Old 02-17-2009, 01:33 AM   #2
An old Tradesmen
Rewards Points: 7,380
Yes, its possible, and happens a lot.
What pressure is your boiler at.
Old 02-17-2009, 01:47 PM   #3
boiler pressure is set to 12-15 psi. The bleeder valves I'm mentioning are the ones at each slant fin unit, 7 per floor. Can they leak air into system even though no water leakage is observed?
Old 02-17-2009, 04:19 PM   #4
An old Tradesmen
If they are automatic ones, yes.
Old 02-17-2009, 04:54 PM   #5
the bleeder valves are manual, I have to physically turn them counter clock wise to purge air & slight water at each slant fin unit. Can the valves still leak in air even though they are closed tight?
Old 02-17-2009, 05:06 PM   #6
An old Tradesmen
Manual valves are ok to use.
Unless they are defective/broke, they don't leak air back in.
Sometimes, depending on how the piping is ran.
You need to purge the line, and then bleed the baseboard.
Old 02-17-2009, 08:36 PM   #7
ok, thanks.... I will repipe boiler/ system this summer as per manufacture recommendations. This website is great..
Tile baseboard with carpet? bpak04 Flooring 2 11-03-2008 12:28 PM
Replaceing Baseboard to curvy wall problem agfrag Carpentry 13 08-29-2008 03:40 PM
convert from gas boiler to electric baseboard marks5894 HVAC 1 10-21-2007 12:22 PM
Need help with finding very wide baseboard Showbiz Carpentry 2 05-28-2007 07:52 AM