HVAC Control - HVAC - DIY Chatroom Home Improvement Forum
Old 09-05-2013, 10:20 AM   #1
Rewards Points: 201
HVAC Control
I am converting my HVAC control to a PLC (AB Micrologix).
I have a Carrier Heat Pump w/ 15kW electric backup. At my thermostat, I have the following connections: R, Y/Y2, G, C, W/W1, O/W2. I want to make sure I account for everything when writing the code for this and I had a few questions.
1) When the Aux. Heat (W/W1) kicks on, does the compressor turn off or continue running? I was always under the assumption that the heat pump still ran, but I came across some documentation online that says the heat pump will shut down when the electric strips come on.
2) Does the compressor lockout (timeout before restarting) take place in the thermostat or in the control board?
3) Does the defrost cycle take place in the thermostat or in the control board?
4) During the defrost cycle, does the control board turn the electric strips on automatically?
Thanks.
phuz is offline   Reply With Quote
Old 09-05-2013, 10:48 AM   #2
Rewards Points: 77
[QUOTE=phuz;1238395]
The compressor continues to run. When the compressor is in defrost the defrost control relays turn on the compressor, switch the reversing valve of the heat pump, turn on the interior electric heating element(s), and stops the condenser fan at the outdoor coil from spinning.
When the aux. heat kicks on it would depend on what the function is. Aux. heat will come on when the heat pump can not keep up with heating the house. It is also supposed to come on to temper the inside air when the condenser goes into a defrost cycle.
The defrost control board
Also depending on the set up, if you have a programmable thermostat you can lockout the heat pump from operating at a certain temperature or lockout the auxiliary heat strips based on your preferences.
firedawgsatx is offline   Reply With Quote
The Following User Says Thank You to firedawgsatx For This Useful Post:
phuz (09-05-2013)
Old 09-05-2013, 11:11 AM   #3
Rewards Points: 201
Thanks.
Does the control board stop the compressor momentarily when switching the reversing valve or does it do it on the fly?
Old 09-05-2013, 12:28 PM   #4
Rewards Points: 77
If the system is defrosting, the outdoor fan will stop running and the compressor will continue to run (making a buzzing or humming sound). The compressor is actually circulating hot refrigerant through the outdoor unit to melt the ice off the system. After a few minutes, the system will complete the defrost cycle, you will hear a "whooshing" sound, the fan will restart, and steam will blow out the top of the unit.
Old 09-06-2013, 05:10 AM   #5
An old Tradesmen
Rewards Points: 7,378
Originally Posted by phuz View Post
Thanks.
Depends on which model you have. Some of carrier's upper end units do shut the compressor off for 1 minute before switching the RV for defrost.
Old 09-06-2013, 06:05 AM   #6
Rewards Points: 201
But the control board on the main unit handles this, right? Not the thermostat?
Old 09-06-2013, 07:52 AM   #7
Rewards Points: 77
beenthere, thanks for the info about the Carrier heat pumps. I'll add that to my notes.
Yes, the defrost control board at the condenser controls the defrost mode actions.
Old 09-06-2013, 08:00 AM   #8
Rewards Points: 201
Great, thanks.
At this point, I am taking over control of the thermostat and don't want to remove any of the controls from the control board itself.
My 15kW electric backup consists of 3 strips and I am thinking about breaking them apart so that I can enable one, two, or three of them using solid state relays, instead of always turning on all 3 when it calls for backup. This will probably be a function of outside temperature, too.
And speaking of outside temperature, where does that signal come back to the inside, and is it a 0-5V signal or thermocouple?
Old 09-06-2013, 08:58 AM   #9
An old Tradesmen
If your unit has an outdoor temp sensor. Its a 10,000 ohm resistance at 77F thermistor.
HVAC Control Problems daveverdo HVAC 1 01-26-2013 05:43 PM
flow control valves jmon HVAC 9 12-12-2012 10:53 AM
Runaround - HVAC and HWH proper venting/exhaust denemante HVAC 24 04-05-2011 08:50 PM
moving HVAC system - can I go without gas for a few days? denemante HVAC 2 03-30-2011 04:55 AM
Moving HVAC system dilemma denemante HVAC 4 03-18-2011 04:55 PM