#1 |
HVAC Condenser FAN Motor hum and won;t start
When I got my AC tune-up done this spring, second unit condenser fan wasn't running. Compressor was running. Little push with a wooden stick to fan made fan started but very slow speed. Tech advised me to get motor replaced as Capacitor is OK. His quote was very high so, I decided to myself. I purchased matching OEM (GE) motor and new Capacitor from Grianger. I had dual capacitor earlier 35/3 and new motor needed 5 MFD, so I replaced capacitor with 35/5 to avoid wiring hassle.
After doing all this situation is still the same. I disconnected Compressor to make sure it is not loading or shorting. Contactor is pulling in and I cleaned rust from all the contacts. Connection - Motor Blue - Contactor where Black is coming from Power, Black to Cpacitor - common (common is connected to contactor with red wire) and Brown to cpacitor - FAN. Kindly advise. |
#2 |
Professional
post a picture of the wiring diagram on the side of the motor on the data plate. Sounds like it is not wired properly.
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#3 |
Thanks, for looking in to it...uploaded file but not sure, so copy paste picture below..
#4 |
You are right hvtech126, I swapped Blue and Black Wire. Motor is running OK but in opposite direction. How do I change direction of motor ?
#5 |
HVAC Condenser FAN Motor hum and won;t start |
#6 |
Thanks a lot, I will have to return this motor and get new one which runs in opposite direction.
#7 |
some motors have external leads that you can switch to reverse them..it appears the motor you have is designed for the direction the arrow is pointing....
#8 |
I just saw in Grainger web site , it is Counter Clockwise. So, I need to buy a motor which runs clockwise.
What if I reverse FAN blades, it should serve the purpose. It is sucking air instead of blowing and reversing fan will change air flow direction. No ? |
#9 | |
HVAC Condenser FAN Motor hum and won;t startQuote:
#10 |
Yes, it is supposed to draw air thro' condenser and out from center to top. But due to it's rotation it is doing opposite.
I can't find a motor which will run clockwise. Original motor was GE 5KCP29ECA091AS. (1/10HP,208-230V, .75A< 1080 RPM, 60HZ, NEMA 42) What I got now is GE 5KCP29CCA341S, with same specification but running in opposite direction. |
#11 |
it should be easy to find a motor that is reversable...
| The Following User Says Thank You to carmon For This Useful Post: | bcjoshi (04-29-2012) |
#12 |
An old Tradesmen
Reverse the blue and brown wires from the motor that attach to the capacitor. It will run the opposite direction then.
| The Following User Says Thank You to beenthere For This Useful Post: | carmon (04-29-2012) |
#13 |
you could be right been... most motors I see here in Canada with a diectional arrow are not reversable... would not be the first or last time I was wrong...
#14 | |
An old Tradesmen
So just changing which 2 motor wires are where on the cap will change rotation. If its a 4 wire PSC, then it doesn't matter whcih wires are where on the cap, rotation will be the same. |
| The Following User Says Thank You to beenthere For This Useful Post: | hvactech126 (04-29-2012) |
#15 | |
| Tags |
condenser fan motor, hvac ![]() |
| Display Modes | |