HVAC Blower Motor Inop. - HVAC - DIY Chatroom Home Improvement Forum
Old 06-18-2012, 09:34 PM   #1
HVAC Blower motor inop.
Hi,
I have a 2002 ICP Tempstar Model# NTG3100GFG1 HVAC unit, the blower fan stopped working yesterday.
The fan does not operate on Cool, Heat or Fan
Using the schematic I traced source voltage to the control board and it's good.
Then I measured voltage at both the "cool" and "heat" fan headers on the circuit board while holding the interlock switch closed. The reading on both headers was around 3V AC
Is this the proper voltage to run this blower?
Thanks for any and all help
Conlan is offline   Reply With Quote
Old 06-18-2012, 09:47 PM   #2
JJboy's Avatar
You need to test the continuity Between W - and W - BK ..... if it is ok the furnace control board is bad.
Doesn't show any led error code?
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
The Following User Says Thank You to JJboy For This Useful Post:
Conlan (06-19-2012)
Old 06-18-2012, 10:06 PM   #3
Thanks for the quick reply
There is no WH/BK wire on this blower motor ...the wire colors are:
1-White
1-Black
1-Red
1-Orange
1-Blue
2-Brown
so I checked continuity between the WH and BK wires and got 1.4 ohms.
There is no LED readout on this unit and the T/Stat is a replacement (Hunter) unit
Old 06-18-2012, 10:18 PM   #4
JJboy's Avatar
1-White - Neutral
1-Black - Cool
1-Red - Unused
1-Orange - Heat
1-Blue - Unused
2-Brown - Capacitor
Check if you have this configuration...... WH - O ( Heat ) should be less the 1.4 ohms.
Conlan (06-19-2012)
Old 06-18-2012, 10:21 PM   #5
Rewards Points: 616
you have me confused.... not hard to do mind you
carmon is offline   Reply With Quote
Old 06-18-2012, 10:47 PM   #6
1-White
1-Black
1-Red
1-Orange
1-Blue
2-Brown
Yessir...that IS my configuration
WH - OG resistance is 2.0 ohms
Old 06-18-2012, 10:52 PM   #7
JJboy's Avatar
Looks like the motor is ok.....check the capacitor......just for make sure....you can hook up the motor by passing the board controller.....
Conlan (06-19-2012)
Old 06-18-2012, 11:06 PM   #8
Oh...I thought you were saying the motor was bad because the resistance was higher than expected. My bad
Not sure how to check this capacitor...any hints?
Also I was wondering....I thought this board had a transformer on it...isn't the blower motor a DC motor? If so, I can only read AC, not DC from the fan control header.
Old 06-18-2012, 11:18 PM   #9
JJboy's Avatar
This is AC motor not DC. You need a multimeter with MFD to check your capacitor.
Conlan (06-19-2012)
Old 06-19-2012, 05:57 AM   #10
The board should be sending 120V to the motor not 3V.
The Following User Says Thank You to Marty S. For This Useful Post:
Conlan (06-19-2012)
Old 06-19-2012, 08:05 AM   #11
Thanks, 3V seemed awfully low to me.
So...since source voltage to the board is OK and I'm only getting 3V @ the "COOL" and "HEAT" board headers w/ the interlock switch closed and the T/Stat in the "Cool", "Heat" or "Run" positions respectively, I can assume that the Blower Fan Relay on the board is defective and need a new board...correct?
Old 06-19-2012, 07:49 PM   #12
I got it figured out
Realizing there is 115V @ the interlock switch, I hooked up the BK "COOL" lead from the blower motor to the load side of the switch, closed the switch and the fan runs.
So, since I can hear the Fan relay "click" (close) but only 3V comes out of the header, I must have a bad relay (board)...I hope...lol
Can anyone recommend a good place to buy one online, I live in the sticks
Thanks for the replies and help.
Old 06-19-2012, 07:54 PM   #13
JJboy's Avatar
If you post a picture or the board controller number will help a lot.
Old 06-19-2012, 08:05 PM   #14
Honeywell # ST9120C4057
HQ1011927HW
Old 06-19-2012, 08:39 PM   #15
JJboy's Avatar
HQ1011927HW
http://www.ebay.com/itm/ICP-Heil-Tem...-/370316863962
Conlan (06-19-2012)
Bryant Plus 90 - No Blower Ducaticorse HVAC 13 01-03-2015 04:39 PM
Help with HVAC blower motor wiring Jcpilot Electrical 4 03-18-2012 02:28 PM
separate switch for blower in HVAC system lettersoup HVAC 3 11-11-2011 10:13 AM
Goodman HVAC system blower stuck on? OhNoes HVAC 14 09-03-2011 07:32 PM
hvac blower vs capacitor, does my conclusion make sense? Lalan64 HVAC 2 07-17-2010 08:24 AM