Condenser motor runs with no call for cooling.changed 2 contactor n still having the same problem. Checked voltage, I am reading 120V on one side,
N nothing on the other side of the contactor. The condenser fan is turning slowly when I plug the disconnect.
I'll appreciate any input.
Aafaissal is offline   Reply With Quote
Old 07-26-2012, 04:45 AM   #2
Does the motor run okay during a call for cooling?
You should read 120v to ground on BOTH sides of the LINE side of the contactor (the incoming voltage), and you should also read 240v across those lines. You must check both of these - don't assume that you have 240, put your meter on it and check it.
This is often caused by a shorted capacitor. You can also check that with an ohm meter - you should have no continuity to ground between any of the cap terminals.
scottmcd9999 is offline   Reply With Quote
Old 07-26-2012, 05:12 AM   #3
An old Tradesmen
Rewards Points: 6,914
Short in the cap, fan motor or compressor.
The Following User Says Thank You to beenthere For This Useful Post:
ben's plumbing (07-26-2012)
Old 07-27-2012, 07:42 PM   #4
There's 240v from the disconnect to the contactor. What i'll like to know is why I'm I reading power across the contactor without the coil being energized.
When I call for cooling the unit works fine. Switch it off and the condenser fan keeps running. but slower this time. The unit is 4months old 410a.
Old 07-27-2012, 07:48 PM   #5
Mad Scientist
The contactor is only breaking one of the two incoming legs, (single pole contactor) and something is shorted to ground. Very dangerous; the metal parts of the condenser unit are probably live at 120V.
McSteve is offline   Reply With Quote
Old 07-27-2012, 08:00 PM   #6
Short as stated above. Got to ask though, if the unit is only 4 months old why are you messing with it instead of calling the installers?
The Following 2 Users Say Thank You to Marty S. For This Useful Post:
ben's plumbing (07-27-2012), scottmcd9999 (07-28-2012)
HELP!!! How much owe my HVAC repairman? Is he competant? MB1 HVAC 23 02-01-2012 02:42 PM
Runaround - HVAC and HWH proper venting/exhaust denemante HVAC 24 04-05-2011 08:50 PM
moving HVAC system - can I go without gas for a few days? denemante HVAC 2 03-30-2011 04:55 AM
History of HVAC Industry Brands winkydink HVAC 8 03-25-2011 07:28 AM
Engineered Joists & holes for HVAC ducts walt1122 Building & Construction 3 07-04-2009 07:37 PM