Humidity Question - HVAC - Page 4 - DIY Chatroom Home Improvement Forum
Old 04-10-2013, 02:56 PM   #46
Originally Posted by beenthere View Post
If your referring to secondary heat exchangers. Boilers don't use a secondary heat exchanger. But all cat III and IV have heat exchangers. other wie they would be direct fired, and not be vented.
All cat III and IV appliances are positive pressure vent systems. So they are power/direct vent systems.
Ok, what about direct vent fire places. Mine has a stainless steel flex line running up the chimney for intake and exhaust. Those don't have heat exchangers do they? Positive pressure just means they are fan assisted venting, right?
mmiller is offline   Reply With Quote
Old 04-10-2013, 03:25 PM   #47
An old Tradesmen
Rewards Points: 7,816
The fireplace would be a Cat I. Is it a fireplace, or fireplace insert.
Fan/blower assisted. The fan is also responsible for creating the draft in the heat exchanger. It may be a negative or positive pressure heat exchanger.
Old 04-10-2013, 04:28 PM   #48
Its an insert. Its direct vent so how can it be Cat I?
Old 04-10-2013, 04:39 PM   #49
Here is another thing I get confused with. My furnace has an induced draft blower. Now that forces the byproducts of combustion out through the exhaust, right? What I don't understand is what is the difference between that and a forced draft blower?
Old 04-10-2013, 04:58 PM   #50
An old Tradesmen
Its vented in a chimney. The chimney liner is the chimney. It doesn't vent through a sidewall. It needs a natural draft chimney.
Old 04-10-2013, 05:00 PM   #51
An old Tradesmen
Your furnace, if an 80% unit. Has a draft inducer. It induces a draft in the heat exchanger. Its not actually a blower. As it requires a negative draft in the flue pipe.
Old 04-10-2013, 05:36 PM   #52
Im confused. The liner that is being used is a double stainless steel flex line. With direct venting I thought that is cat IV and positive pressure in the vent. Is this not the case with fireplaces?
Old 04-10-2013, 05:38 PM   #53
Ok, and what forces the exhaust into the vent pipe? Mine is a 93% unit. 2 pvc pipes for intake and exhaust. These are horizontal so it has to be positive pressure in the draft, right?
Old 04-10-2013, 05:50 PM   #54
An old Tradesmen
Its just a liner. The fireplace is till a negative pressure draft appliance.
Old 04-10-2013, 05:52 PM   #55
An old Tradesmen
Your furnace is a condensing furnace. it is a positive pressure vent furnace. the inducer is a blower. It creates a draft in the heat exchanger, and also forces the exhaust fumes out the flue pipe.
Old 04-10-2013, 06:55 PM   #56
I know you need air and fuel to create proper combustion and I thought that was done at the burners? Why does the heat exchanger need a draft? The pipe leading into my draft inducer is hot so if its creating draft from outside air how is it hot?
Old 04-10-2013, 07:01 PM   #57
An old Tradesmen
The exhaust pipe of your 93% furnace shouldn't be real hot. Less then 140F. Thee is no negative dratf in it. Its under a positive pressure. What little draft would be created in it by the flue gasses being at 140 wouldn't be near enough draft.
The heat exchanger needs a draft through it to keep the gasses moving through it, and not rolling out toward the burners.
Old 04-10-2013, 07:56 PM   #58
The draft inducer that sucks in combustion air is also the same blower that forces exhaust out of the second pvc pipe? I also noticed on my indoor coil there is the obvious incoming liquid line and outgoing suction line. I noticed a third port for another line. Do you think that is for a heat pump?
Old 04-10-2013, 08:01 PM   #59
An old Tradesmen
Yes, it does both functions.
Probably not. Post a pic of it.
Old 04-10-2013, 08:22 PM   #60
how do you post pictures on here?
window condensation kmpittman Windows and Doors 4 11-29-2011 09:10 AM