I have an HAI Omnistat controlling a Trane XE90 and an Aprilaire Humidifier.
Problem I am having is the thermostat only has a single wire for Humidifier control which does indeed activate the solenoid on the humidifier when the humidity is too low. The problem is that it sometimes calls for humidity even if there is no call for heat. I thought the thermostat would call for both Fan and Humidifier in this case; but it only calls for the humidifier. So the humidifier runs without a fan which is useless.
I called the vendor and they said this was normal operation and something would have to be rigged up externally.
My initial thought was to strap the G (FAN) and humidifier wires together but I think that will also kick in the humidifier in the case there the Tstat calls for FAN and doesn't need humidity.
Any ideas on how to accomplish this?
The manual is here:
http://www.homeauto.com/Downloads/Pr...ion_Manual.pdf
Thanks in advance
cipherman is offline   Reply With Quote
Old 11-01-2011, 03:24 PM   #2
An old Tradesmen
Add a relay that is energized by the humidity terminal.
Old 11-01-2011, 03:47 PM   #3
What should the relay switch (I am assuming a NO relay)? I don't think it should switch the fan? Should the relay switch the 24V RC lead to the Fan G lead upon the Humidifier lead activating?
Old 11-01-2011, 03:50 PM   #4
An old Tradesmen
Run a jumper from the furnace R terminal to one contact of the relay, then run a jumper from the other contact(NO contacts) to the G terminal of the furnace. Run the wire from your stat's humidity terminal to one of the relay's coil terminals, and then run a wire from the other coil terminal to the furnace common.
The Following User Says Thank You to beenthere For This Useful Post:
cipherman (11-01-2011)
Old 11-06-2011, 01:58 PM   #5
Ok, ran into a snag. The Thermostat Humidifier Output lead is 24VAC not DC. So it won't operate a relay. Any other ideas on how to get this application working?
Old 11-06-2011, 03:30 PM   #6
An old Tradesmen
All of the Aprilaire humidifiers I install, use 24 VAC.
Old 11-06-2011, 08:33 PM   #7
Thumbs up
Right but relays for switching require DC. I did get it working.
I picked up a rectifier from Radio Shack and used that to convert the 24VAC from the Tstat to 24VDC so that I could activate the relay. The relay in turn switches 24VAC from the W Terminal of the furnace to the Solenoid of the Humidifier.
Here are the parts I used:
Rectifier (I picked mine up from Radio Shack)
http://www.amazon.com/Parts-Express-...ies/B0002KRDPI
Elk Heavy Duty 24V Relay
http://www.elkproducts.com/_webapp_2...arge_terminals
Works like a champ. Now the Omnistat is serving as the humidistat and turning on the humidifier. I decided to only activate the humidifier if the heat is on which is why I am switching 24VAC from W.
Old 11-06-2011, 08:37 PM   #8
An old Tradesmen
The humidifier is suppose to wire directly to the thermostat.
Old 11-08-2011, 10:34 PM   #9
Yes, but this particular thermostat only calls for Humidity and doesn't have a setting to call for Humidity if only there is a call for heat. Hence the external circuit.
Old 12-10-2011, 11:48 PM   #10
MisterTFM's Avatar
why don't you just buy a 24 vac relay vs. 24 vdc?
MisterTFM is offline   Reply With Quote
Aprilaire 700 humidifier wiring installation seanbie HVAC 10 12-17-2011 05:13 PM
Aprilaire 700 Wiring tysonmj HVAC 2 01-31-2011 06:48 PM
Need advice on Aprilaire Humidifier, 2 questions. Maack HVAC 0 12-30-2010 06:49 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 03:40 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 08:52 PM