HRV Duct Sizing Question With Damper - HVAC - DIY Chatroom Home Improvement Forum
Old 04-19-2013, 03:30 PM   #1
Rewards Points: 83
HRV Duct Sizing Question with Damper
I'm trying to design an HRV ducting system and I had a few theoretical questions in regard to using a damper.
I'd like to have two main trunks that come off the HRV: trunk A and trunk B. These two trunks will be pulling the air OUT of the rooms.
Trunk A will serve a kitchen and two bathrooms.
Trunk B will two crawlspaces.
If I place a normally open damper on trunk B, and I energize the damper, the damper will close.
My expectation is that the CFM amount will fall to zero in Trunk B and will increase in Trunk A.
Should I size the Trunk A and the Trunk A branches to accomodate the CFM when the Trunk B damper is closed, or when it is open?
toddmanqa is offline   Reply With Quote
Old 04-20-2013, 04:21 AM   #2
An old Tradesmen
Rewards Points: 6,148
Neither.
Trunk A should be sized to 125% of the air you want to go through it when ever the HRV is running.
Tags
cfm , damper , duct , hrv , size
Duct work sizing for 800 CFM unit mattorrell HVAC 11 03-25-2013 03:01 PM
Bathroom Exhaust Fan Duct Sizing Lyndon HVAC 6 02-06-2012 08:35 AM
Old flex duct question doityourselfer2 HVAC 3 12-05-2011 01:37 PM
Question Re: New Furnace and Duct Sizing DSimo HVAC 3 06-17-2008 08:24 AM
Duct sizing question Rob HVAC 1 06-04-2005 01:42 PM