How To Diagnose A Bad Heatstrip Sequencer - HVAC - DIY Chatroom Home Improvement Forum
Old 08-15-2011, 01:23 PM   #1
how to diagnose a bad heatstrip sequencer
i live in south texas so we dont get A TON of no heat service calls. but i would like to know, how do you properly diagnose a heating sequencer? and what do you check if both heating and cooling come on at the same time when there is a call for cooling?
Final Notice is offline   Reply With Quote
Old 08-15-2011, 05:31 PM   #2
An old Tradesmen
Rewards Points: 6,550
See if it closes when 24 volts applied. then see if ti opens after 24 volts removed. keeping in mind it is a timed device, and you must allow time for it to close, and to open.
Old 08-15-2011, 11:27 PM   #3
Rewards Points: 380
If heat and cool both come on at the same time usually someone has tied into the fan leg without an isolation relay and is backfeeding on W when G is energized. Typical for A/C install on unit without terminal strip. (famous in older mobile homes in my area)
HVACDave is offline   Reply With Quote
Old 08-15-2011, 11:35 PM   #4
what causes the time delay within the sequencer? is it heat build up as current passes through it @ 24V?
Old 08-15-2011, 11:43 PM   #5
JJboy's Avatar
The heat makes the thermocouple close like a on/off switch. So heat will continue building up until close the second stage and so on.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 08-15-2011, 11:47 PM   #6
Rewards Points: 380
When 24 volts is applied to the base terminals of the sequencer it energizes a heater in the bottom of the control. After a period of time (which varies depending on what time delay you purchase from the supplier eg. H 15-30 C 10-20 would mean when 24 volts is applied it will take between 15 and 30 seconds for the contacts of the switches above the heater section to close, which will turn on elements or fan,or energize another sequencer coil, then when the 24 volts is lost it will take 10 to 20 seconds for the contacts to re-open which will result in the elements, fan etc. to shut off.
How to diagnose gas valve problems Nestor_Kelebay How To Guides 28 10-30-2013 05:19 PM
How to best diagnose and repair electrical issue. adamjt Electrical 3 08-29-2010 08:50 PM
old singer electric furnace need sequencer help carpenterbronco HVAC 1 12-29-2009 07:33 AM
Carrier rep coming to diagnose a problem Faulknertw HVAC 14 07-17-2008 12:25 AM
help to diagnose pilotless heater problem jpplumber HVAC 30 01-02-2007 09:11 AM