raineywillow 12-29-2008 09:03 AM

hot water boiler pressure
 
Okay it is me again. I have emptied the expansion tank, all was good for a short while. When the furnace is finished heating up and turns off, the pressure continues to increase to 30 psi, then of course the relief valve releases water, approx. 1/2 pail full.

Any suggestions, or should I call for service?:wink:

SKIP4661 12-29-2008 09:21 AM

If it's not the tank than it is the more than likely the pressure reducing valve (prv) is not regulating properly. This is located where the domestic water connects to the boiler for filling. There should be a gate valve or ball valve near the prv so you can turn the water off to verify the prv malfunction.

hvaclover 12-29-2008 09:28 AM

What is your water temp set up for? Are tripping valve on temp or press.

What is boiler press staying at?