Hot capacitor?
Went to an intermittent no cool call today and came across a capacitor rated for 55/5/440 that tested 54/4.8 so well within specs. It was very hot to the touch which I have never seen before. Do they get hot before swelling up? Replaced it to be safe and the system is working fine now, well fine as it can with a .85 static on a system that lists max external static .5".
beenthere 07-27-2010 05:02 PM
Swelling is usually from over heating. The oil boils/expands and bugles the housing.
Marty S. 07-27-2010 05:15 PM
Thanks beenthere. Did not know that.
yuri 07-27-2010 07:47 PM
Did you check the voltage and amps draw of the compressor? I always do that when changing caps so I don't get callbacks and da Boss saying why didn't you do that. :wink:
Marty S. 07-27-2010 08:24 PM
Sure did yuri. Fan and compressor amps,voltage,capacitor reading,pressures,SH,SC,return temp and supply temp go on every ticket.