Honeywell VR8200H Pilot Ok But No Burner Flame - HVAC - DIY Chatroom Home Improvement Forum
Old 09-03-2016, 04:10 PM   #1
Rewards Points: 4
Honeywell VR8200H Pilot ok but no burner flame
I recently received a used furnace form a neighbor that was converted to propane. I have it connected to propane and the pilot light starts up ok. When power 24vac is supplied to the Honeywell VR8200H 1236 gas valve, I can hear and feel a nice solid click, but there is no gas flow to the burner.
has anyone run into this problem? Solenoid clicks but no gas.
Honeywell specs say this valve is slow opening. How slow would it be? few seconds? milliseconds?
Thanks in advance for your help.
daveinarmstrong is offline   Reply With Quote
Old 09-03-2016, 06:51 PM   #2
Rewards Points: 7,438
Re: Honeywell VR8200H Pilot ok but no burner flame
If this is a standing pilot furnace it could be a faulty regulator in the valve or inadequate gas supply/pressure.
Being propane, i wouldn't mess with it. Call a pro -> it may not even be installed right.
My Backround FIY: I am not in the business of any trade or topic I give advise on. I have some have formal education in HVAC + some DIY experience. Theory is not a substitute for experience.
user_12345a is offline   Reply With Quote
Old 09-04-2016, 12:30 AM   #3
Rewards Points: 3,758
What's the gas pressure set to?
Has the heat exchanger been checked, being its a used unit?
roughneck is online now   Reply With Quote
Old 09-04-2016, 01:36 PM   #4
Rewards Points: 46
Slow in the case means, seconds to about a minute or so. The regulator inside is controlled via gas pressure. So if the inlet pressure is inadequate or the control orfice is plugged, it won't open. Closing is usually immediate. (within a second or 2) The pilot port on the valve has a separate regulator.
The only thing a professional can do is test the pressure to the manifold and see if adjusting the reg makes any difference. The next step is to change the valve. While it's possible to DIY this if you're mechanically savvy, it wouldn't be advisable if you haven't had any training.
Cheers!
supers05 is offline   Reply With Quote
Old 09-04-2016, 03:25 PM   #5
Rewards Points: 4
Thanks for your help. Turns out there was a bad connection inside and one of the coils were not activating. Ill be replacing the valve.
Thanks again.
Tags
honeywell , no flame , vr8200h
Trouble-shooting Flame Rectification Circuit Grounding justplumducky HVAC 10 03-30-2014 01:00 PM
Carrier furnace problem. Pilot lights, no burner Donut HVAC 1 02-09-2011 08:07 PM
Proper color of flame for oil burner ejsharp HVAC 6 10-27-2010 05:17 AM
comfortmaker pilot lights but not burner jasonzzz HVAC 6 01-28-2008 11:20 AM
Utica Boiler Pilot light on but will not flame up! MGB150HID HVAC 2 12-10-2007 04:48 PM