I have a Honeywell TH8320U (VisionPro 8000 Series) TSTAT. The A/C unit is a Trane with AC / and a Gas furnance.
The thermostat (when in heat mode) stays on "WAIT" the entire time heat is requested. Nothing happens for hours, it just says "WAIT"
If I remove the TSTAT from the wall and then select heat, the "WAIT" does not appear and the internal relay clicks on. I can then put the thermostat back on the base unit/ wall the heat will run.
I had an AC tech come out and diagnose the problem. He said he thought it was the thermostat needed to be replaced. I switched it out with another and the same thing is happening, so it must not be the thermostat?
Any ideas?
Thanks!
Mike_DIY is offline   Reply With Quote
Old 10-19-2011, 09:52 PM   #2
Houston204's Avatar
Rewards Points: 556
W or B is shorted to common or ground.
What type of heat do you have?
Houston204 is offline   Reply With Quote
Old 10-20-2011, 07:19 AM   #3
It has natural gas heat.
When the system is in cool, the A/C portion works fine and "WAIT" does not appear.
It is only when the system is selected to heat that this "WAIT" problem shows up.
**UPDATE**
I pulled the panel off the gas furnace and I looked at the circuit board. It was replaced last summer by the same service company due to the A/C not working. They had common (in this case the blue wire from TSTAT) hooked to the W terminal which also had the white wire from the TSTAT hooked to it. I moved the blue wire to the Common terminal on the curcuit board and now the heat is working fine. "WAIT" no longer appears.
I am puzzled as to why they had it wired like that. However, the A/C worked fine all summer despite that.
Any ideas?
Old 10-20-2011, 06:25 PM   #4
Houston204's Avatar
Rewards Points: 556
Probably an accident.
Rheem Heat Pump & Honeywell VisionPRO infoskr HVAC 2 11-20-2013 05:08 PM
Honeywell VisionPro Short Cycling? kcrossley2 HVAC 33 01-19-2011 03:02 PM
Honeywell VisionPro IAQ YTH9421C1002 Wiring Help jond777 HVAC 0 11-22-2010 09:22 PM
Honeywell VisionPro Thermostat infoskr HVAC 32 12-17-2008 03:44 AM
Carrier Infinity Control VS Honeywell VisionPRO 8000 Theromostat super_man4471 HVAC 2 04-26-2007 02:27 PM