Honeywell THX9321R5012 Wiring - HVAC - DIY Chatroom Home Improvement Forum
Old 01-09-2011, 03:00 PM   #1
Honeywell THX9321R5012 wiring
I am replacing an older two wire t-stat with the Honeywell THX9321R5012 t-stat and can't get it to work. I tried the W & R terminals as well as the W & C terminals but no go. Just a blank display. The backplate is stamped with... will not operate without wire to C. If W & R (the two existing wires) are for the heat, and I need to run a third wire for C, what does it tie in to?
sws63075 is offline   Reply With Quote
Old 01-09-2011, 03:32 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
c on control board in furnace. what model furnace do you have?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 01-10-2011, 07:09 AM   #3
It's an old American Standard Sunbeam K-100. No control board on this one. Just two wire 24vac for the t-stat and main gas valve. Blower is large squirrel cage type.
Old 01-10-2011, 08:45 AM   #4
AKA HVACTECHFW
c will be the ground of the furnace
IT IS WHAT IT IS
Old 01-10-2011, 10:16 AM   #5
Rewards Points: 516
Common Wire Names:
R or RH - HEATER TRANSFORMER
W - HEATING CONTROL
G - FAN RELAY
C - 24 VAC COMMON (optional)*
Y - COOLING COMPRESSOR
RC - COOLING TRANSFORMER
O - DAMPER OR CHANGEOVER VALVE (POWERED IN COOL)
B - DAMPER OR CHANGEOVER VALVE (POWERED IN HEAT)
* The optional C-wire should be connected if available, it will extend your battery life significantly.
Alternate wire names:
Most Common Wire Names -
R NEMA power for both heat and cool (sometimes the marking will be R v )
Rc NEMA power for cool (when separate power for cool)
Rh
or 4 NEMA power for heat (when separate power for heat)
W NEMA Heat (sometimes the marking will be W h)
Y NEMA compressor (sometimes the marking will be Y c)
G NEMA fan (sometimes the marking will be G f)
C NEMA Unswitched side of transformer or Common power
O NEMA Heat pump change over powered in cool.
B NEMA Heat pump change over powered in heat.
diyorpay is offline   Reply With Quote
Old 01-10-2011, 02:24 PM   #6
Thanks!
I emailed Honeywells' customer Care Center as well as this chatroom. They replied... The thermostat requires 3 wires for the installation. You must have a wire connected to the R, W and C terminals. The C terminal has its own voltage supplied with the wire to activate the display screen, the R terminal is used for the power from the HVAC system and the W terminal is the heat relay.
If I am understanding this correctly then I need another 24vac line for C. Installing a second transformer just for screen power wouldn't be a bad idea.
Do you agree?
Wiring a Honeywell RA89A Relay shawnmd HVAC 9 10-17-2016 06:52 PM
Honeywell Thermostat Wiring Differences DavidHwang HVAC 16 01-28-2012 02:11 PM
Honeywell Prestige HD thermostat wiring 1H/1C + Humidification System TekGamer HVAC 0 07-09-2010 11:58 PM
Wiring help - Honeywell Thermostat w/ Carrier Heat Pump Tom Williams HVAC 7 09-14-2008 07:40 AM
Trane Heat Pump tstat replacement with Honeywell prog - wiring question sep23 HVAC 2 10-20-2006 09:10 PM