Honeywell Thermostat - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 02-19-2012, 04:44 AM   #16
An old Tradesmen
Rewards Points: 7,284
Your old thermostat was 3 stages of heat, your new one is only 2 stages of heat. So you'll end up having to controll your 2 sages of aux heat off of W2 only.
Old 02-19-2012, 12:20 PM   #17
does that mean two wires to one terminal on new thermostat? I will reply back tonight with models of heat pump. Airhandler is intertherm
cariboulou is offline   Reply With Quote
Old 02-19-2012, 12:28 PM   #18
AKA HVACTECHFW
Rewards Points: 1,208
yes, and yet, maybe no.... The E terminal is confusing as it does not go to the AHU as it normally would. That is the reason we need the HP model number and brand.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 02-19-2012, 02:22 PM   #19
An old Tradesmen
Yes, in order to get the full use of your aux heat package.
You should get the proper thermostat though.
Old 02-19-2012, 09:09 PM   #20
Ok traced both wires from stat and condenser to a/h. Here is the final wiring scheme. from thermostat to a/h: the first letter is the terminal on old stat and wire color:
(L)=grey; connected to nothing in a/h
(X)=light blue; connected to C on a/h
(W3)= pink; connected to W2 on a/h
(W2)= white; connected to W1 on a/h
(R)= red connected to red wire from condenser and wired to a firestat button and wired to R on a/h
(G)= green connected to G on a/h
(O)= orange connected to orange wire from condenser
(Y)= yellow connected to yellow wire from condenser
(E)=brown connected to nothing in a/h, just hanging there
(B) = empty
Here are connections from condenser:
(C)=blue connected to C on a/h
(Y)= yellow conneted to Yellow wire from stat
(O)= orange connected to Orange wire from stat
(W2)= white connected to W1 on a/h
(R)= red connected to red wire from stat and wired to a firestat button and wired to R on a/h
(E)= brown connected to nothing in a/h
the a/h is an intertherm and the outside unit is a nordyne model DT3BA-KA
the honeywell RCT8102A is the new stat I want to install.
Old 02-19-2012, 09:11 PM   #21
BTW the old stat had 2 lights, EM Heat and Aux heat
Old 02-19-2012, 09:38 PM   #22
See the attached wiring diagram.
Jumper W1 to W2 at the AHU.
Jumper Aux and E terminals at the new thermostat. This is shown on page 25 of the RCT8102A manual note 5
thermostat is offline   Reply With Quote
Old 02-19-2012, 11:21 PM   #23
ok, starting to understand what some aux heat and heat come in....is this why to jumper w1 and w2? do i have 2 stage heating?? What about the programming mode on this stat, i should set it up as a heat pump with backup and emergency heat? or just heat pump with backup heat?
Old 02-20-2012, 04:07 AM   #24
An old Tradesmen
No, your system has 3 stages of heat.
Old 03-03-2012, 10:06 PM   #25
Sorry bout delay, finally hooked up and a/c works great! Will check out heat pump this fall, i know emergency heat works but cant really tell about heat pump heat. I was told to listed for a loud hiss when condenser comes on but didnt hear it?
Honeywell RTH111 Thermostat justplumducky HVAC 8 06-11-2011 11:14 AM
Replacing old Honeywell thermostat with new Honeywell thermostat optimizer HVAC 13 04-20-2011 06:22 PM
Honeywell Prestige HD thermostat wiring 1H/1C + Humidification System TekGamer HVAC 0 07-09-2010 11:58 PM
Replacing Honeywell thermostat with another Honeywell flipz HVAC 4 02-06-2010 04:19 PM
Wiring help - Honeywell Thermostat w/ Carrier Heat Pump Tom Williams HVAC 7 09-14-2008 07:40 AM