shawnmd 10-24-2010 07:47 PM

Honeywell L8124L Settings on Oil Boiler
 
My settings on the L8124L slant/fin oil boiler were set at Hi-170, Lo-150 and differential at 25, when would the circluator be running when there is a call for heat in the house?

Also, I have an Superstor Ultra indirect water tank connected as another zone for DHW, are the above settings correct for this type of DHW? Also, I have a wood boiler plumbed into this system, does the above settings seem correct for this as well?

Thanks

beenthere 10-24-2010 08:11 PM

Those settings are fine. I'd use a slightly lower setting with an indirect though. Since you don't need it as high for an indirect. Probably 130 for low.