Honeywell Focus PRO6000 - HVAC - DIY Chatroom Home Improvement Forum
Old 09-30-2011, 09:49 PM   #1
I am installing a programmable thermostat, TH6220D1002. I would like to make sure I am connecting the wires to the correct terminals. The old thermostat (manual) is on the left, the new on the right.
MANUAL ............ TH6220D1002
R ........................ R & RC
O ........................ O/B
C ......................... C
Y1 ....................... y
E/W1 .................... E
G ......................... G
W2 ...................... ???
??? ..................... AUX
The new terminals are obvious for the most part. I am concerned about terminal E/W1 and terminal W2. These terminals are tied together on the old thermostat.
Do I tie together terminal E and terminal AUX on the new thermostat? OR do I leave AUX empty?
namasil is offline   Reply With Quote
Old 09-30-2011, 10:02 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
add a jumper to tie them together on the new stat as well. and jumper Aux to E
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 10-01-2011, 05:50 AM   #3
Actually on that stat the e and aux terminals are energized in emergence heat. No jumper is needed.
In the olden days, the heat pump had an outdoor temp sensor that would lock out the heat strips above a certain temperature. The E feature of the stat was used to bypass the sensor. Modern systems don't use that sensor anymore.
Master of Cold is offline   Reply With Quote
Old 10-01-2011, 06:49 AM   #4
AKA HVACTECHFW
"Install field jumper between Aux and E if there is no emergency heat relay." Page 4 of the installation manual. If you dont do this then when the unit calls for aux heat the system most likely wont keep up and then you would have to manually put it on emergency heat.
IT IS WHAT IT IS
Old 10-01-2011, 07:42 AM   #5
An old Tradesmen
Rewards Points: 7,816
Look at your new thermostat. There are 2 sets of terminal designations. W2 and Aux are the same terminal. Put the old W2 to the new stats W2. And jumper it to E.
Old 10-01-2011, 08:31 AM   #6
What I was saying, is that when you put the stat in em heat, the aux and e terminals are engaged. Here is a pic of my 3h/2c stat. I don't have the ability to seperate the two.
Old 10-01-2011, 11:03 AM   #7
After thinking about this for a minute, the 3 and 4 thousand series requires a jumper, 5,6,7, and 8 thousand don't.
Old 10-02-2011, 05:09 AM   #8
An old Tradesmen
The TH6220 needs jumper, the TH6320 doesn't.
Tags
honeywell focus pro6000 , hvac , th6220d1002
Honeywell TrueSteam wont work! Stewart Daniel General DIY Discussions 18 12-20-2010 07:41 AM
Honeywell Focus Pro 5000 gobob2 HVAC 2 01-27-2010 07:49 PM
Replace Trane Weathertron (Baystat 339) with Honeywell RTH2410 ammiller2 HVAC 0 12-12-2009 09:50 PM
Need a programmable thermostat. LUX or Honeywell. speedster1 HVAC 37 12-06-2009 08:33 AM
new honeywell rth6300b to replace very old honeywell thermostat Designman20 HVAC 2 05-06-2009 04:43 AM