My a/c seems to be working fine, but today is was 98'f.
My high pressure line outside is not hot, the low side is very cool to the touch. After checking 3 neighbors units, all their high pressure lines are pretty warm to the touch. My line seems like its maybe 70-80'f,
and the low side is like 40'f
What could be wrong with my unit ?
Seems to cool the house fine, and the unit runs for maybe 10-15 minutes, then turns off and on as its called for by thermostat.
gixxer1000 is offline   Reply With Quote
Old 07-25-2011, 12:23 AM   #2
JJboy's Avatar
I'm guessing since I don't know the pressures. Restricted condenser coil or Liquid line dryer, if it is installed inside of the condenser.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
The Following User Says Thank You to JJboy For This Useful Post:
gixxer1000 (07-26-2011)
Old 07-25-2011, 12:29 AM   #3
I will check pressure's in the morning...thks..
Old 07-25-2011, 12:32 AM   #4
JJboy's Avatar
Get the temp of the liquid line ( small copper ) after the service valve and before get in the Evap.
Old 07-25-2011, 12:36 AM   #5
Will do...whats the best way to test for temps ? I have an infra red tester or a meter with temp probe (non clamp on type)
Old 07-25-2011, 12:41 AM   #6
JJboy's Avatar
Infra red should be ok
The Following 2 Users Say Thank You to JJboy For This Useful Post:
Doc Holliday (07-26-2011), gixxer1000 (07-26-2011)
Old 07-25-2011, 02:03 AM   #7
30 year tech
hvac122's Avatar
Infra red doesn't always work on copper. Use a strap on thermometer.
hvac122 is offline   Reply With Quote
The Following User Says Thank You to hvac122 For This Useful Post:
Old 07-25-2011, 04:47 AM   #8
An old Tradesmen
Rewards Points: 7,332
Temp probe. IR is unreliable on copper lines.
May not be anything wrong with your system.
The Following User Says Thank You to beenthere For This Useful Post:
Old 07-25-2011, 05:48 AM   #9
Rewards Points: 1,216
If the unit is keeping the proper temps and everything seems in order I wouldn't mess with it.
I would get through the season then at next years startup and maintenance I would have everything checked out.
Maybe all your neighbors units are running hot and yours is normal.
COLDIRON is offline   Reply With Quote
The Following User Says Thank You to COLDIRON For This Useful Post:
Old 07-25-2011, 06:41 AM   #10
biggles's Avatar
your condenser is the cleanest of the group the Liquid Line should be slightly warm body temp but it it's hot the condenser isn't being removed and it goes into the air handler on the liquid line....the line right off the compressor to the top of the condenser now that one on a full charge you can't touch...
The Following User Says Thank You to biggles For This Useful Post:
Old 07-25-2011, 12:12 PM   #11
How old is your compressor ? The small line should be around 100-110 if outside ambient temp is 98. Does the air blow out of the condenser hot like your neighbor's ?
clocert is offline   Reply With Quote
The Following User Says Thank You to clocert For This Useful Post:
Old 07-25-2011, 12:26 PM   #12
Rewards Points: 338
the liquid line is high pressure not high heat. the whole point of the condenser is to take the very hot high pressure gas that comes out of the compressor and cool it down to a warm not-as-high pressure liquid as it exits the condenser. my liquid lines are typically only slightly warmer than ambient. you should have hot air blowing out the top as the fan extracts the heat from the line.
if the line is too hot something is wrong.
NitroNate is offline   Reply With Quote
The Following User Says Thank You to NitroNate For This Useful Post:
Old 07-26-2011, 06:22 AM   #13
biggles's Avatar
the heat difference from the compressor line and the liquid line is what blows in your face....if it is little above ambient on a 90F day your condenser is clean
Old 07-26-2011, 06:57 PM   #14
Finally got around to test out the pressure's and temperatures.
It was 87'f outside today.
73'f inside the house.
The temperature of the high line (1/4") was 76'f before the valve.
The temperature of the high line (1/4") was 109'f coming out the compressor.
The temperature of the suction line (3/4") was 61'f before the valve.
The temperature of the high line (3/4") was 67'f just before the compressor.
The pressure was 75 psi on the suction line (3/4") with unit running.
The pressure was 240 psi on the high line (1/4').
The air temperature coming out the registers in the house was about 55'f
Does this seem correct ? Or should it be colder coming out the register.
There is about 25-30 ft. of copper line coming from outside to up in the attic.
Old 07-26-2011, 07:07 PM   #15
JJboy's Avatar
Sounds good. Grab a beer and forget about AC
ac not cooling, suction line freezing, suction pressure in "Retard" GetYourShineBox HVAC 7 05-26-2011 09:01 PM
lennox xp15 high pressure fault code GEAF HVAC 10 03-11-2011 08:44 PM
High pressure Shower Head Carloscda Plumbing 9 06-18-2010 12:50 AM
Running a secondary high pressure line Randell Tarin General DIY Discussions 6 02-18-2008 11:39 AM