-   -   high line freezes (http://www.diychatroom.com/f17/high-line-freezes-148819/)
lasey-JANE 07-01-2012 02:16 PM
high line freezes
i installed a new compreessor in my rheem 3 ton heat pump it worked great for a day the n it quit cooling and the high pressure line is freezing up what is the problem
beenthere 07-01-2012 02:27 PM
Did you change out the filter drier.
lasey-JANE 07-01-2012 02:40 PM
high line freexes
no i didnt
beenthere 07-01-2012 03:28 PM
good chance thats where he problem is.
lasey-JANE 07-01-2012 05:26 PM
high line freezes
how can i replace the drier without draining the freon can i isolate the freon
JJboy 07-01-2012 05:27 PM
pump down the refrigerant inside of the condenser :thumbsup:
beenthere 07-01-2012 05:27 PM
have to recover it if the drier is inside the cabinet.
lasey-JANE 07-01-2012 05:50 PM
high line freezes
how do i pump freon into the condenser i am not sure
JJboy 07-01-2012 06:11 PM
close the high service valve until the low gauge shows 0 psig.....close the low service valve
After you replace the dryer filter you have to leak test with nitrogen at 150 psig and them vacuum until micro test hit 500 micron....
beenthere 07-01-2012 07:47 PM
Do you have an EPA cert to handle/work with refrigerants?
scottmcd9999 07-02-2012 04:32 AM
Where, exactly, is the high pressure line freezing up? Do you see this on the indoor coil, for example, or somewhere on the outdoor unit?
Note that if the drier is INSIDE the condenser cabinet, you can't pump the refrigerant into the condenser. You'll have to recover the refrigerant, replace the drier, and then recharge. As beenthere said, if you don't have an EPA card you should not be doing this.