Old 02-23-2010, 06:45 AM   #16
An old Tradesmen
Rewards Points: 6,124
Temp setting over shoot can be caused by the air filter. Not often though.
It can slow the air flow enough that by the time the thermostat is satisfied. The heat of the heat exchanger is enough that it over heats the house.
You should check the temp difference at the furnace.
If you don't have thermometers that can do that. Then the next best thing is to check it at the supply and return that are closest to the furnace.
If your getting 70 at the registers. You have more then that at the furnace. And your temp rise is TOO high.
The Following User Says Thank You to beenthere For This Useful Post:
mferguson0414 (03-05-2010)
Old 02-23-2010, 06:48 AM   #17
Rewards Points: 85
I will look into that some time this week and get back with ya, maybe my finding will help someone else out too. i know for sure though that the temp at the furnace and the temp at the closest register should be close, that air out of the register is HOT!
mferguson0414 is offline   Reply With Quote
Old 02-23-2010, 06:50 AM   #18
An old Tradesmen
Most furnaces want a temp rise(at the furnace) of less then 70F with a new clean air filter.
Old 02-23-2010, 06:52 AM   #19
Rewards Points: 85
Is temp rise calculated from measuring the temperature when the unit first kicks on to when it kicks off during the cycle? You are quick to respond on these threads by the way.
Old 02-23-2010, 07:10 AM   #20
An old Tradesmen
No. After about 3 to 5 minutes of the blower running, you can check the difference between the return and supply temp.
Somedays it takes me hours to respond, other days a few minutes.
Old 02-23-2010, 07:22 AM   #21
Rewards Points: 85
What type of thermometer would you suggest in this application?
Old 02-23-2010, 07:25 AM   #22
An old Tradesmen
Some oven thermometers will read the supply temp(need to be able to read as low as 100F, and upwards of 150F). And then you can use a regular room thermometer for the return air temp.
Furnace filter brands to avoid? MistyLee HVAC 10 11-09-2015 07:01 AM
Water Inside/Around American Standard Furnace michrob HVAC 8 12-08-2011 04:51 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 02:45 AM
Furnace minus filter dsal HVAC 16 02-24-2008 01:26 PM