Help With New T-stat (B, E, R/H) - HVAC - DIY Chatroom Home Improvement Forum
Old 06-12-2014, 10:51 PM   #1
Rewards Points: 18
Question
Help with new t-stat (B, E, R/H)
Ok I have a HVAC unit and I am replacing the t-stat.
Here are the current wire hookups and there discription on the old t-stat (Robertshaw 9420).
C-Blue ~24v Com
R-Red ~24v Transformer
Y1-Yellow ~Compresser Relay (Stage 1)
E-Black ~Emerg Heat
W2-White ~Aux Heat Relay (Stage 2)
G-Green ~Fan
B-Orange ~Heat Active Reversing Valve
Unused:
L-N/A ~System Monitor LED
Y2-N/A ~Cooling Relay (Stage 2)
O-N/A ~Cool Active Reversing Valve
Here is the termanals on the new t-stat (EcoBee) and my assumed wires:
Y-Yellow ~1st Cooling
W(O/B)-Orange ~1st Heating (or Changeover)
G-Green ~Fan
W2(AUX)-White ~2nd Heating (or 1st Aux Heat)
R/H-Red?? ~Heat transformer return
R/C-"" ~Cool transformer return (Jumpered to R/H by default)
ACC1-Black ~1st accessory relay (Emerg Heat)
ACC1r-Red ~Jumpered for power
ACC2-White2 ~2nd accessory relay (Dehumidifier)
ACC2r-Red2 ~12v from Dehumid relay(+)
ACC3-White3 ~3rd accessory relay (Humidifier)
ACC3r-Red3 ~Jumpered for power
IN1(+)-N/A ~Alt Dehumidifier
IN1(-)-N/A ~Alt 12v from Dehumidifier relay(+)
I'm not sure about the "B-Orange~Heat Active Reversing Valve", I know that messing this up can ruin your comp. What should go in R/H(&R/C) just 24v, or am I missing something? Also where should I put the Dehumidifier? The Dehumid has its own 12v DC relay for 120v power, so I know I don't want to send it 24v AC, but should I use a dry contact (IN1), or an accessory slot (ACC2)?!?
KzBoy is offline   Reply With Quote
Old 06-13-2014, 04:39 AM   #2
An old Tradesmen
Rewards Points: 7,400
Is it battery only operated?
The orange that is on B of old stat, goes to W/O/B of new stat. new stat has to be told to energize it in heating mode. Connect your dehumidifier to dry contacts.
Old 06-13-2014, 07:33 AM   #3
Rewards Points: 18
No, its 24vac, I assume that it's fed from the 24v transformer (old C & R). sorry, I forgot to mention that. That's where some of my confusion concerning R/H came from, do I need to jumper between Red on R/H & 24v AC input?
Old 06-13-2014, 05:47 PM   #4
An old Tradesmen
Would need to see the wire diagram/instructions of teh thermostat to say for sure.
Old 06-13-2014, 06:12 PM   #5
Rewards Points: 18
ecobee[DOT]com/wp-content/themes/ecobeev2/files/manuals/IMR1-290611_ENG_V23web.pdf
^^^Install manual - ecobee
Old 06-13-2014, 06:31 PM   #6
An old Tradesmen
Okay. Yeah, the R and C are connected to the R and C from the transformer. And you will need a wire from R to RH and the jumper from RH to RC.
Old 06-13-2014, 07:02 PM   #7
Rewards Points: 18
Great, thanks for all your help!
Old 06-13-2014, 11:23 PM   #8
Rewards Points: 18
Ok, I think I'm all up and working. Had a small problem with the 24vac "RETURN", I mistakenly assumed the 24vac FEED (+) would be the main. Apparently HVAC systems switch on the neutral (BIG no-no in the standard AC/DC world I'm used too).
I have cool air flowing and have dropped 3-deg in the last 30 min or so. YAY!
Now I just wait until winter and see if the heat, Aux heat, Emrg heat, and Dehumid are working. ;-P
Old 06-14-2014, 04:15 AM   #9
An old Tradesmen
Technically, it has no true + or -. Also no neutral. 24 VAC on an HVAC system has a common.
Tags
dehumidifier , ecobee , emergency heat , har valve , relay
need help upgrading manual merc stat to new digital stat tlb813 HVAC 3 08-13-2012 12:31 PM
new stat wiring help chongololo HVAC 4 05-05-2012 06:25 PM
T stat with 2 wires on 240? OffRoadAudio Electrical 6 12-13-2011 06:52 PM
Replacement Thermostat Problem! Confuserated HVAC 8 03-26-2010 08:17 AM
LUX digital stat Trane XE80 intermittant problem rossl56 HVAC 6 12-26-2008 05:53 AM