Help Needed - Goodman GPG10 Burner Won't Stay Lit - HVAC - DIY Chatroom Home Improvement Forum
Old 01-19-2011, 07:14 PM   #1
Unhappy
Help needed - Goodman GPG10 burner won't stay lit
I have a Goodman GPG10 2 ton gas pack unit that is 5 years old. On Monday, I replaced my draft inductor motor and fan assembly, as the motor had siezed up over the weekend. The new motor was not a direct replacement, as the original equipment one was discontinued. The replacement was nearly identical, with the only difference being that there was only one power wire instead of the two on the original (208V & 230V)After replacing the draft inductor and hooking everything back up, now the burners won't stay lit.
The system does the normal 15 second purge and the electric ignitor preheat. When the gas valve opens, only the bottom burner (this is a two burner model) lights. After a few seconds, the gas valve closes and the system recycles with another purge and then relights the burners. This second time, the upper burner also lights but as soon as it does and the flame hits the flame sensor, the gas valve shuts off again. This cycle will repeat several times until it finally shuts down completely. Each time the system cycles, the LED indicator on the control board flashes once.
To troubleshoot this, I checked the connections at the control board and sensors and all seemed good. I removed the burner tubes and checked for blockage and none was found. I removed the burner orifices and checked for blockage and none was found. I removed the flame sensor and cleaned it with steel wool. None of these items corrected the problem.
I am wondering if the new draft inductor motor is running at a different RPM, causing the airflow across the burners to be higher, as the flame seems to be pretty intense when it lights. If so, I would assume that the gas pressure would need to be adjusted, which would require a professional.
rhayward is offline   Reply With Quote
Old 01-19-2011, 08:25 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
clean the burner crossovers and faces and while you are in there clean the flame sensor
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 01-19-2011, 08:37 PM   #3
Thanks for the reply. I will do those checks tomorrow, but I am puzzled why the system worked perfectly OK all winter and I only started having the issue after changing the draft inductor motor/fan.
Old 01-19-2011, 08:50 PM   #4
AKA HVACTECHFW
coincidence?
IT IS WHAT IT IS
Old 01-19-2011, 09:48 PM   #5
Rewards Points: 516
Check p 52 here:
http://www.fasco.com/documents/fascopage51-59.pdf
http://www.fasco.com/documents/fascopage22-30.pdf
Hopefully still have old id fan/motor to match up.
Older links: http://www.fasco.com/pdf/p22.pdf
http://www.fasco.com/pdf/p58.pdf
Watch for clockwise and counterclockwise spin.
diyorpay is offline   Reply With Quote
Old 01-21-2011, 07:59 PM   #6
I ended up calling a service tech out from the local HVAC company that sells Goodman products. He cleaned and adjusted the burners to get the flame to light consistently. However, it still wouldn't stay lit. It turns out that the control board was bad because it did not sense the flame. I must have damaged it when I was plugging in the new draft inducer motor or maybe it was overloaded when the old motor froze up. I will never know. The important thing is that the heat is back up and running.
monitor heater repair help speakers3 HVAC 16 01-18-2015 04:00 AM
Homart (Sears) gas forced air, pilot won't stay lit. OLD TIMER NEEDED diyjohn HVAC 5 12-07-2011 09:15 PM
Help Needed. Goodman furnace jzw HVAC 14 01-01-2011 11:21 PM
bryant gas furnace burner wont stay on. pipebender HVAC 29 11-08-2009 07:41 PM
Furnance burner won't stay on. 2007ken HVAC 11 03-03-2008 11:29 PM