Old 08-29-2012, 09:13 PM   #1
Question
Help me troubleshoot my heat pump; it's mostly working...
Here's the summary:
I started having some problems and read through a fair number of threads on this forum to see who has run into similar problems. I eventually found that my symptoms exactly matched the symptoms of having a bad contactor. That is, the thermostat would turn the system on and off as it should, but the outside compressor unit would never engage. When I took the compressors panel off to start poking around (and looking for bad capacitors), I found that if I pressed the contactor, it would start right up! Problem solved, right?
The wrinkle is: I replaced the contactor, and still have the same problem.
What should I troubleshoot next?
Some more ramblings:
To get around the contactor not working, I just ran the wire around it and bypassed it. So that the unit doesn't run all the time, I just use the circuit breaker inside to turn it off and on manually. Not ideal, but it is able to cool the house down when needed. One concern I have is that I may be bypassing some sort of safety mechanism. Perhaps the unit is designed not to run if the coolant level is low, or something, and I'm forcing it to run?
The unit is about 7 years old. It's nothing fancy and was replaced through a home warranty, which only had to be better than the (20+ year old) unit they were pulling out, so you know it's quality (). It looks like it might be a Payne PH10 (PH10JA036-J)
The capacitor didn't look bad. I work on computers for years, so I've seen bad ones, and this one looked fine. But, I didn't measure it with a volt meter or anything. Should I?
A few possible problems I can see:
The thermostat isn't controlling things like it should, even though it seems like it is. (Possible. It's a Hunter 44760. Maybe 6 years old, nothing fancy)
The contactor I put in was bad, too (bought from a service department of a local HVAC service company)
I wired the new contactor in wrong somehow (but I only swapped one wire at a time...)
Some other control element is bad, somewhere along the way?
Thanks for any thoughts, and thanks already for the troubleshooting tips I already read!
IckesTheSane is offline   Reply With Quote
Old 08-29-2012, 09:27 PM   #2
When T-stat call for AC, and contactor does not respond, you need to check if you have power (24V) at the contactor terminal. If it does, then you have a bad contactor, if not, you have other problems.
clocert is offline   Reply With Quote
Old 08-29-2012, 10:31 PM   #3
Yes you need to check for 24 volts at the control terminals at the contactor when the thermostat is supposed to be calling first and you could be endangering the unit because one of the safeties may have it off it is probably not low pressure however as your house probably would not cool down. You may have a bad safety or your high pressure may have tripped on a hot day. is the coil clean and is there a red button somewhere around on the small line going from the compressor to condensor coil. I am not that familiar with Payne to know their control setup we don't see many around here.
Originally Posted by IckesTheSane View Post
Here's the summary:
marcusjson is offline   Reply With Quote
Old 08-30-2012, 12:13 AM   #4
Excellent! I don't know why I didn't think to check the voltage earlier. That'll be on my to do list for tomorrow, and I'll get back to you.
If you're a fan of typing, or speculating: If the contactor isn't getting the voltage it needs, what would be some other parts to look at?
It does cool the house, so if it's low on coolant, it doesn't seem _that_ low.
Marcusjson, I don't recall seeing a red button anywhere. Would this be on the coolant line, or is it electrical? There is a fair amount of the line that is concealed, but accessible (drop ceiling), though I'm guessing it would be close to one end or the other. If I have a bad safety or I tripped a high pressure sensor, is there a way I can tell?
Thanks for your help! I'll let you know what I find!
Old 08-30-2012, 02:28 PM   #5
If 24V is not there, you need to check the transformer and control board (both of them are in the air handler).