Heil Ignition Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 01-26-2008, 07:08 AM   #1
Heil ignition problem
I have a 1 year old Heil 90+ which is intermittently failing to fire. The first attemp the ignitor burns, the gas valve opens, the burners ignite and stay lit for 1 second then go out. The second attempt fires appropriately and stays lit and the entire cycle is complete. The furnace can work correctly for a couple of days and then the above problem occurs. Any idea what is causing this burner to go out at times? I've changed the flame sensor already and don't believe it is the thermostat. I do get a diagostic LED of 6 flashes (flame sense lost while running) when it is happening. Should I be concerned about leaving town for a couple of days?
Brickman is offline   Reply With Quote
Old 01-26-2008, 08:28 AM   #2
Union HVAC Tech.
Well if that's the code your getting, it's a flame sensor problem. Take a good look at the wire going to the sensor, is it damaged, insulation nicked anywhere? Are the crimped terminals tight? Ohm it out with a meter and see if it has any resistance, if so swap it out.
bigMikeB is offline   Reply With Quote
Old 01-26-2008, 03:31 PM   #3
The wire is fine (no apparant breaks or nicks) and fastened tightly. No resistance with Ohm meter. Note per prior message, the flame sensor was switched out 5 weeks ago and this did not fix the problem. The 6 flashes appears only when ignition lights and then goes out. After the next try, it stays lit and works fine with the LED flashing the usual soft heartbeat. Could it be the ignitor?
Old 01-26-2008, 05:24 PM   #4
Union HVAC Tech.
You can just time the igniter, a good one lights in less than 45 seconds from energizing.
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 07:01 PM
This may help someone with carrier ignition problems AweMan HVAC 15 02-09-2009 01:20 PM
Heil problem with gas valve Frank4711 HVAC 1 12-14-2007 10:03 PM
Heil ignition problems sky jumper HVAC 1 11-16-2007 12:30 PM
HEIL 5000 Furnace Problem moore70 HVAC 5 03-26-2006 07:59 PM