Old 01-17-2012, 07:36 PM   #16
Temp Rise 40 - 70 F
JohnnyV is offline   Reply With Quote
Old 01-17-2012, 07:40 PM   #17
I'm Your Huckleberry
Rewards Points: 2,270
140 minus 69 would equal 1 degree over max temperature rise ALL due to restricted return air. The limit switch is working.
Clear the returns.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 01-17-2012, 08:03 PM   #18
how
Rewards Points: 1,102
I'm guessing that you probably did your temp rise test with the drapes away from the return air grill & the remodel problems sorted out so you still have a furnace temp problem.
All you've determined is that your limit is working on a furnace that is running too hot.
You can clock your gas meter to see if the furnace is overfired.
See if there is a higher speed tap to use on your blower.
Check the other possible causes of an air flow restriction that have already been posted here.
or call a pro.
how is offline   Reply With Quote
Old 01-17-2012, 08:11 PM   #19
How - Excellent suggestions
Thank you again!