Heil 5000 Furnace - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Old 04-21-2013, 09:22 AM   #31
OK I got 25.4 volts to red, or PV the pilot, the pilot fires up but i only get 8 volts to Black or MV. when the pilot goes out all voltage drops to O
Rchevy61 is offline   Reply With Quote
Old 04-21-2013, 09:37 AM   #32
Hvac Pro
yuri's Avatar
Rewards Points: 1,846
then the S86 ignition control is faulty or the gas valve is draining the voltage. check with the wire off the valve. either way you got a $200 problem. the new S86U/ universal is TRICKY to install as they changed some of the wiring terminals and terminology and you need to read the install info VERY VERY carefully.
The Following User Says Thank You to yuri For This Useful Post:
ben's plumbing (04-21-2013)
Old 04-21-2013, 09:52 AM   #33
would it light if i switched the red and black around? I only need this thing for a few more weeks? I got a new one coming in June.
Old 04-21-2013, 10:05 AM   #34
Hvac Pro
yuri's Avatar
DO NOT EVER start switching things around. If it loses it's flame then you will blow up the house as you will have NO flame failure protection.
Old 04-21-2013, 10:34 AM   #35
Can it be manual fired just to get the chill out during the spring?
Old 04-21-2013, 11:20 AM   #36
No. Go buy a space heater or two to knock off the chill.
The Following User Says Thank You to Marty S. For This Useful Post:
Old 12-29-2013, 04:09 PM   #37
Heil 5000 furnace
I've read the previous posts, but they don't exactly address my problem.
When I turn the 'stat up so the unit will start, the fan starts, the igniter sparks, and a puff of pilot gas ignites, but the pilot light goes out right away. This sequence will repeat itself every few minutes (until I turn the 'stat down to off). I've checked all electrical connections and the unit worked a couple of days ago. What's my next step? Thanks.
Bozak is offline   Reply With Quote
Old 12-29-2013, 05:58 PM   #38
Experienced HVAC Tech
HVAC1000's Avatar
Originally Posted by Bozak
I've read the previous posts, but they don't exactly address my problem. When I turn the 'stat up so the unit will start, the fan starts, the igniter sparks, and a puff of pilot gas ignites, but the pilot light goes out right away. This sequence will repeat itself every few minutes (until I turn the 'stat down to off). I've checked all electrical connections and the unit worked a couple of days ago. What's my next step? Thanks.
clean the flame sensor. It is in the same "cluster" or assembly that the little aluminum pilot tube terminates. It looks like a little thick wire that sticks out in front of the pilot hood. Use a wire brush or scotchbrite pad to clean off wire. While u are at it clean of sparking igniter rods. They look just about the same as flame sensing rod
HVAC1000 is offline   Reply With Quote
Natural Gas Cost For Furnace 1 Hour Run Time hammerlane HVAC 25 01-14-2015 02:13 PM
Heil 1990 furnace and Roll Out Switch jimdwest HVAC 12 02-09-2013 06:24 PM
Heil Furnace driving me insane - and broke! Drider75 HVAC 43 02-04-2013 06:41 AM
American Standard 5000 gas furnace PyrateJim HVAC 20 01-05-2011 01:48 AM