Heat Tripping Breaker - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-14-2013, 06:15 PM   #16
Rewards Points: 77
Your problem probably lies with the part of the electric strip that you can't see without removing it. Here is a photo of a typical heat strip. The coils can touch each other and short out causing the circuit breaker to trip. The photo shows what is involved as far as which part would be replaced. Replacement strips are readily available and less costly than a lot of manufacturers. Due to 240V being involved, it can be extremely dangerous/deadly if you don't know what you are doing.
firedawgsatx is offline   Reply With Quote
The Following User Says Thank You to firedawgsatx For This Useful Post:
beenthere (10-14-2013)
Old 10-14-2013, 07:40 PM   #17
An old Tradesmen
Rewards Points: 6,458
Originally Posted by Shadetree99 View Post
Sorry for the delay. I have since replaced the thermostat. Heat strips are still receiving current in cool mode. Do you think it circuit board or transformer in the pic causing the issue?
If everything is wired correctly, and working correctly. You will still read voltage with the way that you have that meter connected.
Disconnect all low voltage wires from the control board, and see if the heaters still come on then.
Old 10-14-2013, 08:17 PM   #18
Rewards Points: 77
Disregard my last post. I failed to notice there were two different posters on the same thread.
Shadetree99 (10-18-2013)
Old 10-18-2013, 08:49 AM   #19
mechanic by trade
First let me say THANKS to you both for trying to help. This unit belongs to my sister and I am just trying to help her out.
beenthere: Please help me understand. The original issue was the heat strips are receiving power while in cool mode. Based on your response I am drawing the following conclusions:
1. The thermo change could have fixed the issue.
2. The circuit controls the ground to the strips and not the positive.
3. I could check both leads to a strip for closed circuit test.
4. If I still have closed circuit to strip, disconnect low volt circuits from board to test for board failure?
Thanks a million !!
Shadetree99 is offline   Reply With Quote
Old 10-18-2013, 05:44 PM   #20
An old Tradesmen
Yes.
There is no ground to the strips themselves. They are 208/230/240 volt, so no ground connected to them.
Best to do an amp draw check, on both sides of the element. Even when energized, you will read full line voltage across the strip as it is a load.
Thanks a million !!
Yes, next step is to disconnect low voltage control wires and see if the strip is still being energized. If so, the sequence/delay board may have its contacts burnt closed.
Old 10-21-2013, 10:16 PM   #21
mechanic by trade
I reconnected everything and the heat strips still have constant current. When I disconnected the low voltage circuit from the strips (See Connector unplugged) The strips remained energized. Could the issue be the relays I have marked in the picture? It is the only thing I see that could energize the strips. I am thinking the overheat protector in the top of the picture might be bad as well. Your thoughts?
Thanks.
Old 10-22-2013, 05:36 AM   #22
An old Tradesmen
The middle relays could be stuck/burnt fast.
When you check to see if they are still energized. You are reading 240 volts on them, and not just checking from one end of the strip to ground, correct.
Old 10-22-2013, 06:21 AM   #23
dmxtothemax's Avatar
Rewards Points: 5,100
Can you post a picture of the wiring diagram ?
We need to be sure that your reading the voltage in the right way.
What voltage are the heat strips,
And how are they controlled,
You said that they switch the neutral line,
If there on 240v then there is NO neutral.
Only two hots !
Need to see the wiring diagram to be sure !
And YES relays can stick in the on position.
dmxtothemax is offline   Reply With Quote
Old 10-23-2013, 03:13 AM   #24
Rewards Points: 1,192
Howzabout the o/b setting on t'stat?
bobelectric is offline   Reply With Quote
Old 11-06-2013, 08:06 AM   #25
mechanic by trade
Just wanted to post a resolution and a HUGE THANKS to all who chimed in here. Your collaborative efforts led me to follow logic and find the issue and I have gained valuable knowledge. It turned out to be the top relay in the center of the above pic. It was fused and allowing constant current to the heat strips. Thanks again to all. My sister thanks you since she now has heat ! I hope this thread will one day help someone else to a quicker resolution.
The Following User Says Thank You to Shadetree99 For This Useful Post:
beenthere (11-07-2013)
Heatpump vs Natural Gas - Energy Cost Spreadsheet zootjeff HVAC 11 06-22-2015 04:59 AM
Heil Electric furnace tripping breaker chrishosley HVAC 31 02-26-2013 07:35 PM
How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? twilightcall HVAC 34 12-28-2010 07:53 PM
HW tank breaker tripping arichard21 Electrical 6 10-31-2007 05:13 PM