#1 |
Heat tripping breaker
My A/C runs fine. Problem is with heat. On a cold night if I crank up the thermostat the breaker will trip. If I reset and only raise the thermosat a couple of degrees no problem. Than when I reach the set temp i again raise another couple of degrees. No problem. Only trips when I raise the temp say 6 OR 8 DEGREES AT A TIME. lOOKS LIKE THE AIR HANDLER IS ON A DOUBLE POLE 30 AMP BREAKER AND THE OUTSIDE UNIT IS ON A DOUBLE POLE 20 AMP BREAKER IF THIS HELPS.
tHANKS. |
#2 |
Hvac Pro
Is it a heat pump? Post the brand name and model and serial #. If it has extra electric strip heaters in the ductwork one may be shorted and causing the problem. They cut in when the temp has dropped or the heat pump cannot keep up.
"Cut it twice and it is still too short". To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#3 | |
Heat tripping breakerQuote:
Appreciate the reply. Unit is made by Goodman manufacturing Houston, TX. Only three years old. Unit inside house says heatpump/ac unit. Model number is ARUF182416AA Serial Number is 0607203217. Where are these heat strips located? Can I fix myself or do I call an HVAC professional. Never heard of Goodman. If I had put in unit would have gone with a better know name but it was installed just before I bought house. Had home inspection done but not sure if inspector checked heat as inspection was done in May. Thanks again Jay |
#4 |
Electrical Contractor
Check the kW rating of that air handler/strip heat. A 30 Amp breaker would be good for 5 kW or so. Many units have 10 kW strip heaters, which would blow a 30 Amp breaker in short order.
So the question now is this: Does the breaker trip immediately, or take a few minutes after you bump up the heat setting by more than a few degrees?
-KB Life is uncertain -- eat dessert first!! To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#5 |
Hvac Pro
You should get a Pro to do it. Those strips use 240 volts and if shorted one slip can kill you. May have 5 yr warranty on parts but 1 yr on labor. Goodman is a very large company. Got a lot better recently when they joined with Amana. VERY popular with new home builders due to reasonably priced equipment. Not hard to get parts for.
#6 |
Thanks, Yuri. The breaker takes a couple of minutes to trip. I see no KW rating on unit. There is a plate which indicates minimum amperage if "auxillary heat kit" is installed however none of the listed aux. heat units are checked on the plate. Ill look up the model on Goodman site. I hope its a short in the strip and not too small a braeker as this would be quite expensive to rerun a circuit I imagine. Yuri, when HVAC pro did the original wiring hookup wouldnt they assure the breaker was of adequate size??
#7 |
Hvac Pro
You would hope so. Possible that no permit was taken out or inspection done. Another reason to get a Pro to check it out properly.
#8 |
An old Tradesmen
The model number of the air handler won't tell you what strip kit is in it.
Need to look to know. |
#9 |
Where is the strip kit located??????????????
| Display Modes | |
| Heil Electric furnace tripping breaker | chrishosley | HVAC | 31 | 02-26-2013 07:35 PM |
| Heatpump vs Natural Gas - Energy Cost Spreadsheet | zootjeff | HVAC | 8 | 11-19-2011 11:45 PM |
| How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? | twilightcall | HVAC | 34 | 12-28-2010 07:53 PM |
| HW tank breaker tripping | arichard21 | Electrical | 6 | 10-31-2007 05:13 PM |