Heat Pump Starts Initially But Will Not Come Back On To Maintain Temps - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Old 10-07-2011, 02:52 PM   #31
I do have a dual fuel configuration, and I do have an outdoor sensor on the side of the outside unit. I will trace and check the wiring. If there a way to check the sensor (ohms??)?
johnniebravo is offline   Reply With Quote
Old 10-07-2011, 07:03 PM   #32
There are too many hypotheticals going on here. Let's pick one problem area and start there.
You found 26v on the y terminal, and the condenser wasn't running. That's a malfunctioned defrost board. That will have to be replaced. You can wire the unit to test this theory if you wish, but you will not have the defrost option. Although the weather forecast for your area looks like you wont need any defrosting this weekend.
The thermostat jumping temperature after a short run duration could be a faulty stat. Or you could have air from the hole in the wall behind the stat. Couple that with the outdoor temp not reaching lock-out temp, and you have a cold house.
But I would start at the condenser and go from there.
Master of Cold is offline   Reply With Quote
Old 10-07-2011, 08:11 PM   #33
Agreed with the multiple theories, though I do appreciate all of the suggestions. I turned the heat on for the evening since the temp will drop overnight. Hopefully when I get up tomorrow the fan will be running. If it is I will check the voltages at the board and go from there.
Old 10-08-2011, 08:11 AM   #34
Got up early this morning and sure enough the temp had dropped and the system had run all night. Headed outside to remove the panel but first saw that one of the components in the compressor area was frozen. I have a picture but don't have a place to host it.
I proceeded to check the voltage of the yellow wire at the defrost board and it was registering a steady 26.70v (at the Y wire).
I then checked for voltage to the contactor from the two blue wires that feed into the side of it (to the coil??) from the defrost board and they didn't have power.
Lastly, I checked the voltage from the board to the two yellow wires (i still don't know the accurate name of this sensor/switch) and it was getting 26.50v. I also checked the ohms and it was OL or 0.000. Don't know if that means anything.
Link to pictures on Flicker
http://www.flickr.com/photos/johnniebravo2011/
Old 10-08-2011, 09:33 AM   #35
Y energized at board,pressure switch closed and no low voltage at contactor means you need a new defrost control board. Get that replaced along with the defrost sensor.
Old 10-08-2011, 10:10 AM   #36
Yes, time for a board..
Old 10-08-2011, 11:14 AM   #37
OK, tomorrow I will place an order for the following:
ICM304 Defrost Board
DT1172766 ICP Defrost Thermostat
and while I am in there I will also put in a new contactor.
And before the cold sets in I will have a Pro come out and check my refrigerant levels.
So I can better understand what's going on, why is the one particular part of the system freezing rather than the whole outdoor unit? My assumption the board is not telling the system to defrost??
Old 10-08-2011, 11:17 AM   #38
The part that is freezing looks like the txv(im on a mobile phone right now, I can't enlarge it).
The outlet of the txv assembly is the coldest part of the system.
Old 10-08-2011, 12:28 PM   #39
JJboy's Avatar
tvx restriction, power head should be stuck
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 10-08-2011, 12:39 PM   #40
Will a new board and the sensor fix this?
Old 10-08-2011, 12:52 PM   #41
If your heating performance is good, don't worry about the txv.
The only other check would be to check the voltage at the contactor. I know you checked the blue wires at the contactor coils, but those are on the common side. I wold check the other side of the contactor.
Old 10-08-2011, 01:18 PM   #42
There are only contacts on one side of the contactor, the other side doesn't have leads similar to those that connect to the coil.
And yes, the system heats very well when that particular part is not frozen.
Old 10-08-2011, 01:39 PM   #43
JJboy's Avatar
Maybe the check valve inside of txv is good in heating, but not the metering device in cooling......I'm no sure or the check valve is inside of the filter?????
Old 10-08-2011, 02:04 PM   #44
He has good heat when it runs. He is just running too long. The coil gets too cold and the txv shuts down. The little refrigerant that comes through is freezing at the orifice.
Old 10-13-2011, 05:49 AM   #45
With recent weather conditions I don't have much of an update. I replaced the defrost board (ICM304C), I don't know the part number for the defrost thermostat so i have not changed it yet. All the parts online look nothing like the one my unit uses.
After a bit of thinking about the logic behind this system, if in fact the board is bad, it would explain why the system no longer auto switches to aux heat. If a defrost cycle is never initiated it never gets the signal to switch.
As soon as the weather allows, I will be back with feedback.
Tags
compressor , heat , pump , thermostat
Heat pump vs in floor heat mugen HVAC 5 03-02-2010 08:18 PM
Getting a House..heatpump or no? DavidsCPU HVAC 10 02-07-2010 10:22 PM
Heat Pump Blower always on gg_daman HVAC 1 12-16-2009 06:15 AM
Which diagram to use on Lenox Thermostat wiring setup? Heat Pump Lenox techs needed twilightcall HVAC 1 08-13-2008 11:49 AM
Testing FuelMaster 21 Module? Heat Pump no Run. thehotrod11 HVAC 3 12-29-2007 02:11 PM