Old 04-20-2011, 04:17 AM   #46
An old Tradesmen
Rewards Points: 6,498
Originally Posted by JJboy View Post
So to charging 13 seer or higher: calculate subcooling. Measure the high side pressure at the liquid-line service valve pressure tap. Using a pressure temperature chart, convert high side pressure to saturated temperature. Then simply subtract the liquid-line temperature from the saturation temperature of the refrigerant in the condenser to determine the subcooling.
You got it.
The SC showing in the doc is ok to lower than 13 seer.
12 SEER would be over charged using the charging method that DOC showed. And I've seen more then 1, 10 SEER that was over charged using what that DOC showed for getting SC close.
Old 04-20-2011, 07:07 AM   #47
Hvac Pro
yuri's Avatar
Rewards Points: 1,412
JJ here is an install manual for a 13 SEER Lennox unit. Read it carefully and it walks you thru charging an AC with several methods.
http://tech.lennoxintl.com/PDFs/506635.pdf
Old 04-20-2011, 07:11 AM   #48
Post one for a xc21 yuri so he can see the difference in required SC.
Old 04-20-2011, 09:44 AM   #49
Do you mind explain how you do SH and SC?
Subcooling is easier I find as long as you have the right temperature conditions. Just simply get a temp probe on the liquid line out of the condenser and take your liquid line pressure and get the corresponding saturated temperature on your gauges.
Superheat depends on a few more things.
Hubcap626 is offline   Reply With Quote
Old 04-20-2011, 10:40 AM   #50
Am I correct that this system is a fixed orifice valve system?
Ed C is offline   Reply With Quote
Old 04-20-2011, 11:29 AM   #51
Hvac Pro
yuri's Avatar
Here's one for a 17 SEER and a 21 SEER ($6500 and up for those bad boys).
http://tech.lennoxintl.com/PDFs/506585a.pdf
http://tech.lennoxintl.com/PDFs/506587a.pdf
Old 04-20-2011, 11:31 AM   #52
Hvac Pro
yuri's Avatar
Beenthere should know as he is a Yorkie and should be here later.
Old 04-20-2011, 12:28 PM   #53
JJboy's Avatar
WOW. I have a lot material to study. Let me see if I can understand this SC finally. Thank All
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 04-20-2011, 07:07 PM   #54
An old Tradesmen
Standard in 2001 for York from the factory would be a piston. If it has a TXV, then someone splurged and installed it in the field.
Trane Heat pump capacitor exploded! swiffy25 HVAC 18 01-19-2011 06:48 AM
heat pump / ac unit vs electric furnace ellebt HVAC 4 01-12-2011 10:22 PM
Using Gas heat during Defrost mgroves HVAC 15 12-18-2010 06:51 PM
Heat Pump Woes Zenica HVAC 50 01-27-2009 08:37 AM
Which diagram to use on Lenox Thermostat wiring setup? Heat Pump Lenox techs needed twilightcall HVAC 1 08-13-2008 12:49 PM