I woke up the other day to a smell and smoke coming out from the kitchen ac vent. I went and check the ac unit and shut it off. I notice that the heat coils are coming on when the ac unit stops. The coils are located on top of the inside unit. I remove the top to look at the coils, I started the unit and ask my wife to move the thermostat up and the coils got red hot. Can someone plz help.
jkv 09-10-2012 08:51 AM
Sounds like your sequencers are energized.
Meloman 09-10-2012 09:03 AM
Is the sequencer the one that have the wires connected to the coils?
jkv 09-10-2012 09:52 AM
Yea there will be 4-5 wires connected to each side and mabe two or three sitting side by side depending on how many heaters you have.
Meloman 09-10-2012 10:06 AM
Ok I'm going to remove it now then going to pick a new one. I'll keep you in touch, and thanks a lot for your help!
Meloman 09-10-2012 02:13 PM
Ok I got a new sequencer but still the heat coils keep coming on. I remove the top part of the vents to look inside,I notice the bottom heat coils are the ones coming on. Any other suggestions?
jkv 09-10-2012 02:36 PM
do you have a multi- meter? That you can check ohms,volts ect. how many sequencers are on your furnace? Is the stat set to cool? What type of furnce do you have? You will have to back up and check the stat on your wall to see if it is calling for cooling or heat and work your way back.
Meloman 09-10-2012 03:52 PM
Yes I do have a multimeter, what I notice on the old sequencer is that looks like it was melting. The unit have 4heat coils,2on top 2 on bottom, the bottom ones are the only ones coming on. There's only one sequencer for the unit. The brand name of the unit is a janitrol. What I'm suppose to check on the stat? And I really appreciate you taking your time to help me!!
Meloman 09-10-2012 04:07 PM
Does the power needs to be on to check the stat?
jkv 09-10-2012 04:14 PM
Need to know what you read between red and yellow and red and brown, did you make a diagram of the wires when you removed the old sequencer so they are placed just like they were?
jkv 09-10-2012 04:16 PM
Check it in the cooling mode
Meloman 09-10-2012 04:17 PM
Ok,the only thing is I don't know which setting to use on the multimeter,lol!!
jkv 09-10-2012 04:19 PM
put it on volts
Meloman 09-10-2012 04:36 PM
Ok I did it says 0 when I test the yellow,and 0 for the brown.im using the ACV setting.
jkv 09-10-2012 04:44 PM
If you are in cooling mode you should read 0 and 24-27 vols between red and brown your stat sounds bad as well, if you put a new stat on be sure to shut down the power, breaker on the furnace so you dont blow it out