Old 01-21-2013, 05:03 PM   #1
Member
 
sktn77a's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 259
Share |
Default

Heat pump condensers freezing over


Hello all: Having a strange problem at our house. It's on a lake in Virginia (humidity?) and when the weather gets cold (freezing or just above) both of our outdoor heat pump condenser units are freezing over. I could understand it being a fault if only one were freezing over, but both of them? They are both Carrier 38YCC36 (3 ton) outdoor units new in 2005 but not heavily used (the house was someone's vacation home until we bought it last year). We had the charge checked and the defrost board replaced on the downstairs unit.

Any ideas?

sktn77a is offline   Reply With Quote
Old 01-21-2013, 05:14 PM   #2
Member
 
Join Date: Nov 2007
Location: Nashua, NH, USA
Posts: 6,936
Default

Heat pump condensers freezing over


Are there any adjustments for "calibrating" the defrost cycle? (refer to instructions)

Did the serviceman who replaced the defroster board verify that the defrost cycle was actually working after that?

__________________
Stop wasting time re-adjusting the pattern. Have several lawn sprinklers, one for each pattern.
AllanJ is offline   Reply With Quote
Old 01-21-2013, 05:21 PM   #3
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 24,839
Default

Heat pump condensers freezing over


Check what the defrost timer is set to. If its at 90 minutes, set it to 60 and see how it does. If 60 set it to 30.

High humidity will cause heavy freezing.
beenthere is online now   Reply With Quote
Old 01-21-2013, 05:24 PM   #4
Member
 
sktn77a's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 259
Default

Heat pump condensers freezing over


There is a defrost cycle adjustment but I don't remember what it is set at. I'll check on that.
sktn77a is offline   Reply With Quote
Old 02-04-2013, 08:04 AM   #5
Member
 
sktn77a's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 259
Default

Heat pump condensers freezing over


Checked the defrost cycle times yesterday. There are three choices - 90min, 60min and 30 min. Both condensers were set on 30 min so unless neither consenser is working properly (Highly unlikely, I would think, on both units), any ideas what else could cause both systems to freeze over? (They weren't solid blocks of ice but they were pretty much covered with frost, top to bottom and inside to outside and not working efficiently (aux heat coming on, outside temp above freezing).

Thanks,
sktn77a is offline   Reply With Quote
Old 02-04-2013, 08:08 AM   #6
Member
 
Join Date: Nov 2011
Location: Hartfield VA
Posts: 26,248
Default

Heat pump condensers freezing over


Dirty inside filters, dirty slant coil in the air exchanger?
Just a guess.
joecaption is offline   Reply With Quote
Old 02-04-2013, 03:49 PM   #7
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 24,839
Default

Heat pump condensers freezing over


Yep, check indoor coils and air filters. may have a leak in both units. Seldom happen to 2 at the same time, but it is possible. Are you still having lots of high outdoor humidity days?
beenthere is online now   Reply With Quote
Old 02-04-2013, 05:43 PM   #8
Member
 
sktn77a's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 259
Default

Heat pump condensers freezing over


Thanks guys. Temps have changed a little - colder and, therefore, maybe drier? The units weren't freezing over this weekend but the pipe coming from the outside coil to the compressor had frost on it. Filters are clean; outside coil looks clean (can't really see between the fins but inside and outside are clean as a whistle). Can't get to indoor coil but it was inspected by the HVAC company twice last year and has had clean filters ever since.

Guess I'll have to call them out again (sigh).

Keith
sktn77a is offline   Reply With Quote
Old 02-05-2013, 04:27 AM   #9
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 24,839
Default

Heat pump condensers freezing over


Not unusual for that pipe to have frost on it when its colder outside.

beenthere is online now   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat Pump Efficiency Help! horseonthefly HVAC 5 03-16-2012 04:14 PM
Heat pump is not running on Heat mode frank06 HVAC 17 03-13-2012 03:34 AM
Can I connect Honeywell Vision PRO 8000 (1 Heat/ 1 cool) to a Heat Pump w/aux for heat coils? TimDavis HVAC 12 01-18-2012 07:06 AM
How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? twilightcall HVAC 34 12-28-2010 06:53 PM
New Heat Pump..questions? ddave23 HVAC 4 03-05-2010 05:13 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.