Old 03-03-2011, 09:38 PM   #1
Heat Pump blowing warm air after T-Stat change
Rheem Heat Pump & Air Handler - Just replaced the old Thermostat with a new Honeywell programable Thermostat -
Now I have warm air blowing on the cool cycle - Connections are as follows, and are the same as the old T-Stat, but I'm having problems.......
R - Red
Y - Yellow
O/B - Orange
G - Green
Aux - White
E - Brown
What Am I not seeing or doing wrong here?
ericivins is offline   Reply With Quote
Old 03-03-2011, 10:28 PM   #2
Change the O/B setting or switch to B. Rheem/ Ruud energizes it in heat, all other mfr's energize in cool.
Old 03-03-2011, 10:34 PM   #3
So take the Brown to the O/B terminal? Where would the Orange go?
I just went through the Thermostat and made sure all the settings were correct.......
Old 03-04-2011, 07:17 AM   #4
Professional
bump.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 03-04-2011, 07:19 AM   #5
Professional
No, the honeywell stat needs to be programmed to operate the O/B terminal in heating. This is done in the install setup portion of programming the new stat.
IT IS WHAT IT IS
Old 03-04-2011, 07:22 AM   #6
Put it in cool then feel the large copper line coming from the heat pump. If the pipe is cold and still blowing warm air from the air handler then there's a short in the thermostat wire causing an element to run when it shouldn't. If the copper line is hot then the O/B setting is wrong.
How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? twilightcall HVAC 34 12-28-2010 07:53 PM
Comparison and Heat Pump Selection help... ChrisDIY HVAC 7 03-06-2010 09:34 PM
New Heat Pump..questions? ddave23 HVAC 4 03-05-2010 06:13 AM
Water Source Heat Pump installation JLMitchell HVAC 6 11-30-2009 04:23 AM
Heat Pump set back GEAF HVAC 6 01-26-2009 08:49 AM