-   -   Heat does not turn off with new VisionPro (http://www.diychatroom.com/f17/heat-does-not-turn-off-new-visionpro-83390/)
HoneyPro 10-08-2010 01:17 PM
Got a new Honeywell Truesteam and VisionPro IAQ installes a few months ago on my RUDD. A/C worked great during the summer but with the recent colder weather I noticed the heat doesn't stop once it goes on, even if everything is turned off on the t-stat.
I either have to switch it to A/C and then stop it or turn it off at the braker.
Actually if I tunr off the braker and turn in back on right away the heat is still going. I know it's the heat and not just the fan because the house keeps getting hotter.
Could it be a wiring issue or a programming issue with the VisonPro?
Thanks for your help
moondawg 10-08-2010 01:27 PM
Sounds like a stuck relay inside the VisionPro, to me.
beenthere 10-08-2010 06:52 PM
Probably miswired.
HoneyPro 10-13-2010 10:09 PM
How do I go about testing and finding out which one it is? I've read numerous posts and I would say the wiring is OK. It was done by a professional (but it was his first EIM). How do I know which colors coming from the HP and the furnace are what?
beenthere 10-13-2010 10:24 PM
Look what wires are connected where. And post that info here.
HoneyPro 10-13-2010 10:35 PM
Here goes...
From the HP:
red to RH
black to C
orange to out 1 and green to out 2 for outdoor sensor
blue to O/B
yellow to Y
white and black are free
From furnace:
red to RC
white to C
green to G
blue to aux1
yellow to O/B
From humidifier:
white to hum1
black to hum2
From t-stat:
orange to 1
black to 2
red to 3
beenthere 10-13-2010 10:42 PM
Generally. Whote of the furnace. Should go to W/aux of the EIM. Presuming that its connected to the W of the furnace.
Apparently, they did not wire your heat pump to bring the furnace on for defrost.
gibhvac 10-13-2010 11:21 PM
Sounds like it didn't get programmed correctly for the application you are trying to run. When a tstat that works on heat pump and gas systems are not programmed correctly it will act like you have explained. Also make sure stat is wired correctly too. Good luck.
gibhvac 10-13-2010 11:54 PM
From this the wiring is not correct. If you need heat I would eliminate the accessaries for now until a tech can come out and check it. If u can't wait for tech wire up for normal application and go in and reprogram the vision pro for the app you are using.
Ususally orange is O/B on stat- outdoor and air handler are wired to orange
White is white w1/aux
Red to rh
Use blue for common
Yellow to yellow
Green to green and gets wired on air handler for indoor fan. Not needed on outdoor unit
If you have 2 stage cooling. Use black outside and at stat.
When you confirm all is wired to correct terminals. Reprogram vision pro for the application type. The first few settings are most important and if set wrong will not work correctly. Let me know if you need more help.
From the HP:
red to RH
black to C
blue to O/B
yellow to Y
From furnace:
red to RC
white to C
green to G
blue to aux1
yellow to O/B
From humidifier:
Who wired this thermostat? Looks like that's your problem to start with.
Yellow is used for compressor- Y
Green is indoor fan. No green hooked up outside. G
Orange is reversing valve. O/B
Red is power. Rh or R on stat. Leave jumper in place. Don't remove.
White is heat. Or W1
Common. Use blue in and out.
Everything is color coded and should match up colors
Is this a gas furnace or heat pump. Split unit or package unit?
*** turn off power to units when changing wiring. And you would be wise to go through programming the stat to make sure it's correct. If not it will keep you scratching your head .
white to hum1
black to hum2
From t-stat:
orange to 1
black to 2
red to 3[/QUOTE]
HoneyPro 10-15-2010 04:39 PM
Not sure how to go about this anymore. So far I got replies saying it can by a stuck relay, wrong wiring, or wrong configuration.
Anyway I can test which one it could really be?
beenthere 10-15-2010 05:26 PM
Write down where all the wires are connected at each device, and post it here.
HoneyPro 10-16-2010 02:02 PM
From the HP:
red to RH
black to C
blue to O/B
yellow to Y
From furnace:
red to RC
white to C
green to G
blue to aux1
yellow to O/B
From humidifier:
white to hum1
black to hum2
From t-stat:
orange to 1
black to 2
red to 3
beenthere 10-16-2010 03:55 PM
You said the house kept getting warmer. Did it show that the temp was increasing on the stat, or did the stat just show the temp not rising.
Who ever wired it, was a comedian. Most people would use the same color code from each piece of equipment where ever possible. However, its wired ok. Except, the heat pump is not wired to use the aux heat during defrost.
gibhvac 10-16-2010 05:00 PM
From how I am reading it- its not wired correctly. I will list what doesnt match up from what I am reading.
Blue to O/B- shouldnt Orange from O/d unit and Air handler go to Orange on stat. This is for orange- not blue
white to Common- shouldnt whatver is used fro common on o/door unit and air handler be the same color. If black is used for common at heat pump then black should be used for common on air handler too. and at the stat. Black to Black to black for common.
White needs to be used on W1 at furnace, white to white on outdoor unit and white to aux on stat. They have yellow going to O/B on stat. Orange goes there.
Take blue off of O/B and dont use it
Take Yellow off O/B on Furnace- Orange should go there and at the stat. Use Orange to Orange on HP.
All wires need to match colors. its not as difficult as you think.
This is what you need to have
Thermostat:
Red to RH
Yellow to Y
Black to C
White to Aux
Orange to O/B
Green to G
Furnace:
Red to red
Yellow to Yellow
Black to common
White to W1
Orange to Orange
Green to Green
Heat Pump
Red to Red
Yellow to Yellow
Black to Common
White to White
Orange to Orange
No Green needed. Disconnct that wire for now to eliminate that outdoor sensor for time being until a tech can rewire this system.
Follow the above and you will have heat and it will work correctly. Your wires are for sure crossed with th info you have given. Let me know how it turns out.
beenthere 10-16-2010 05:05 PM
O/B stands for Orange or Blue(blue is most often used with Rheem/Ruud heat pumps, since they energize the RV for heat).
Yes, its better if the same color wires are used at all connections. The equipment only cares that the wires make the correct connection, not that the color is a certain color..