I want to install a Goodman All fuel board in my GMH9590 furnace. I don;s have an issue with the wiring but I do not know where or how to mount the board in the cabinet. I have been looking all over the net for a picture but couldn't find one. Any help appreciated
kilejo is offline   Reply With Quote
Old 10-27-2012, 07:20 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
a OT18-60 is a outdoor thermostat for use in a heat pump outdoors. Do you mean AFE18-60A? It is Goodman's all fuel board and is mounted external to the furnace cabinet. http://www.totalairsupply.com/files/...anual_9-06.pdf
The AFE18-60A should be installed on the side of the furnace
close to the 24Vac controls wires for field connections.
I would recommend a thermostat with a dual fuel control as part of the thermostat instead of using the all fuel board and outdoor thermostat.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 10-28-2012, 04:37 AM   #3
Thanks . You're right I quoted the wrong model number. It is the AFE18-60A. I actually have the manual already.
The AFE18-60A should be installed on the side of the furnace close to the 24Vac controls wires for field connections.
The 24Vac connections are inside the cabinet so it seems to me it is saying it should go inside the cabinet. It just seems like to me that you would not leave a circuit board outside a box of some sort.
As far as using a Tstat that can do duel fuel control, I'm not doing that because the money is already spent and I can't take the AFE18-6A or the the outdoor thermostat back for a refund.
Old 10-28-2012, 06:20 AM   #4
Mount it wherever you want. Most of the time duel fuel controls are screwed to the exterior of the return duct.
Old 10-28-2012, 06:34 AM   #5
Really? Not in any kind of enclosure? How do you keep it from collecting dust? BTW Thanks. I appreciate all help given.
Old 11-08-2012, 03:33 PM   #6
Bill Star
If you are running a dual fuel heat pump/gas furnace set up, with an AFE18-60A dual fuel control board, you may want to be able to by pass the heat pump and run the furnace. These boards use an outdoor thermostat mounted in the heat pump for change over.
The problem with this set up is it is usually set to run the furnace at around 40 degrees outside temperature or less.
What happens if the heat pump fails? How can you get the furnace to kick in?
The control board does not have this ability.
The simplest way is to install a DPDT (double pole, double throw) toggle switch wired to the outside thermostat. The switch will simulate an under 40 degree condition allowing the heat pump to shut off and the furnace to run.
Wire the left side NO contacts across the NO and Com of the stat and the right side NC contacts in series with the NC of the stat and the control board. When the switch is in the down position, it is in the normal mode and in the up position, it will allow the furnace to run.
Bill Star is offline   Reply With Quote
Old 11-08-2012, 06:12 PM   #7
An old Tradesmen
Rewards Points: 7,356
Just switch the stat to emergency heat. then the furnace will be used instead of the heat pump.
The Following User Says Thank You to beenthere For This Useful Post:
hvactech126 (11-08-2012)
Old 11-08-2012, 06:32 PM   #8
Bill Star
If you have a Honeywell zone controller, you can use standard thermostats because the control only outputs the y connection to the all fuel board when set up for heat pump operation. So, if you already have a system as I described, this is the only way to over ride, using a toggle switch.
You are right, however, that newer installations now utilize heat pump stats with the dual fuel capability already built in and do, indeed, have an emergency heat option, as you describe.
Tags
all fuel , goodman , heat pump hvac , ot18-60
Trane XL-80 Control Board got wet.... brandnewrock8 HVAC 10 07-11-2012 03:47 PM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 06:43 PM
Connecting Ledger Board to Vertical Stud Alzipski Building & Construction 3 11-04-2009 02:53 PM
Goodman 4 flashes on control board bigmac71201 HVAC 6 09-28-2009 02:53 PM
DIY recommendation for Goodman Control Module (Circuit Board) njwaves HVAC 3 09-26-2009 07:29 AM