#1 |
Goodman light blinks 3 times
I have a Goodman model GMP075-3 Rev A furnace that won't start. The control panel trouble light blinks 3 times indicating a pressure switch problem. I spent $40 today for a new one and there is no change after I installed it. You can hear the panel kick on but nothing else happens. The trouble light starts blinking after about 5 seconds. Do I need a new blower motor or is there some other issue?
#2 |
30 year tech
If the inducer motor is comming on then check the hoses and where they connect from the pressure switch. Coroosion or small spider webs sometimes will block it from working properly. Also check your vent for blockage like a bird or something.
#3 |
The inducer motor does not come on. Nothing comes on. As soon as I turn the furnace on you can hear the control panel fire up and then NOTHING except for the blinking light. I checked the vacuum hose as well as the vent pipe and all are clear.
#4 |
fabrk8r
The inducer motor may be seized. Check to see that it spins freely. It's a common problem on Goodmans. If the inducer doesn't spin freely the furnace will lock out. Usually there is some warning that the bearings are seizing because they will make a racket, but occasionally they do just stop suddenly.
"The physician can bury his mistakes, but the architect can only advise his clients to plant vines." -- Frank Lloyd Wright |
| Display Modes | |
| Extend a circuit/draw power from light | Ontario | Electrical | 3 | 03-23-2010 07:41 PM |
| Model#PG036100-1A Goodman gaspack won't light | Impala63 | HVAC | 21 | 02-22-2009 10:54 PM |
| Goodman gmp075 4 won't light | Steve72 | HVAC | 7 | 02-06-2009 06:38 PM |
| Adding second light switch to an existing light | TexasEd | Electrical | 7 | 08-15-2008 07:22 PM |
| Whirlpool Microwave light issue | mustangcobra44 | Appliances | 8 | 08-14-2008 04:52 PM |