Old 10-07-2009, 06:51 PM   #1
goodman heatpump
I have a goodman heatpump that will not start. I have checked that the high voltage is correct coming into unit, I also have checked low voltage at unit to make sure unit is calling and it is, I have checked uf on the capacitor and it is good, I also have checked voltage in to contactor and it is good, I can manual energize the contactor and units compressor and fan will run but contactor will not energize on its on.
tarheelhvac is offline   Reply With Quote
Old 10-07-2009, 07:19 PM   #2
GC/Master Plumber/Mech
goodman heatpump
The only thing I didn't see is that you ohmed out the pull in coil on the contactor
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 10-07-2009, 08:35 PM   #3
goodman heatpump
plumber could you walk me thru how to do that
Old 10-07-2009, 08:56 PM   #4
goodman heatpump
The contactor has two wires coming from the furnace. These two wires usually connect on the side of the contactor. DISCONNECT POWER TO THE CONDENSER
Then remove the two wires and set the DVOM to ohm and connect one leads off the meter to the to terminals and measure the resistance
Also what was the voltage to the contactor on these two wires
Old 10-07-2009, 11:21 PM   #5
goodman heatpump
Plumber I already had the contactor out thinking this is my bad part so I couldn't get the voltage on side terminals but I got 17.4 when I ohm the side terminals.
Old 10-07-2009, 11:43 PM   #6
goodman heatpump
The two wire connecting to the contactor should be around 24 volts ac. One wire is 24 vac and the other is the common or ground back to the control board. If on a call for the condenser to operate then taking the DVOM and setting it to ac voltage measuring between the two wire you should get 24 vac.
So what is your voltage
Old 10-08-2009, 08:50 PM   #7
goodman heatpump
Plumber I am getting no voltage to the 24 volt terminals on side of contactor. I notice the right side blue wires go back to the low voltage and the solid yellow and yellow with a blue stripe are going to limit switch off of compressor.
Old 10-08-2009, 09:59 PM   #8
goodman heatpump
Post model and serial number so I can try and get a wiring diagram
Old 10-08-2009, 10:42 PM   #9
goodman heatpump
goodman model gsz130241ab
serial 0905133746
Nordyne condenser goodman A-coil wtroger HVAC 10 09-16-2009 04:52 AM
Evaporator coil for Goodman A/C leschuler HVAC 2 09-25-2008 01:43 PM
goodman furnace nhicks HVAC 3 02-09-2008 07:25 PM
Replacing an 20 year old gas forced air with a 95% 2 stage goodman, goodman 40" tall, englewood1 HVAC 12 09-26-2007 12:37 AM