Goodman GMS90703BXA - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-03-2009, 01:46 PM   #16
There is 27 vac at C and R, the fuse is ok and noticed that if the fuse was blown the LED would not work
ew&se is offline   Reply With Quote
Old 10-03-2009, 01:49 PM   #17
Hvac Pro
yuri's Avatar
Rewards Points: 178
Check my post above yours, this is going fast and I keep editing as I think.
Old 10-03-2009, 02:40 PM   #18
What's the best way to test the ignitor, and do you know if the board would be under warranty?
Old 10-03-2009, 03:02 PM   #19
Hvac Pro
yuri's Avatar
Rewards Points: 178
The igniter gets turned on after the inducer starts and press switch and limits are proven. If the inducer is not on then no power to the igniter. You can check it with an ohmeter but need to know the ohms of a new one. Not all igniters use 120 volts nowadays. Read the warranty info in the owners manual or call your dealer.
Old 10-03-2009, 08:04 PM   #20
I was able to pick up a new board covered under warranty. I put all the wires back but as soon as I powered up the machine the fuse blew.
Old 10-03-2009, 08:48 PM   #21
Hvac Pro
yuri's Avatar
Rewards Points: 178
Without being there I cannot really help you too much further. You may want to call a pro in before something gets damaged further. Sounds like you have a short somewhere.
Old 10-03-2009, 08:53 PM   #22
I pulled all the individual wires off to see which on blows the fuse and it was a black wire that goes to terminal XFMR. Do you think I may have put the wires back wrong? I'm going to double check if there is any worn out insulation on any wires.
Old 10-03-2009, 08:57 PM   #23
Hvac Pro
yuri's Avatar
Rewards Points: 178
XFMR = transformer and is the 24 volts hot. I would take the wiring diagram and carefully follow it. I use a pair of 1.4x WMart reading glasses and they prevent "errors".
Old 10-03-2009, 09:17 PM   #24
I diconnected all the wires from the tstat and the a/c and reattached the xfmr and it didn't blow. I think you're right it might be the tstat. Any ideas on what I should check next?
Old 10-03-2009, 09:36 PM   #25
I jump the r and w and the furnace started. I reattached the blue and red wire to Y, the white to C and Green to G and the fuse blew. I guess this means my tstat is bad?
Old 10-04-2009, 01:06 AM   #26
I tested with the Red thermostat wire connected to the R on the furnace board, and with any other wires connected even the White common from the A/C unit made the fuse blow. I disconnected the the old tstat and wire, and wired in another one to the furnace. This tstat was the one my HVAC guy took off and said it was causing an earlier problem about a year ago. I wired it in myself because I couldn't get him to come back and finish the job. It seems to be working fine both A/C and furnace. Now I guess I have to check the wires or maybe I should just put the new tstat in?
Old 10-04-2009, 08:58 AM   #27
Hvac Pro
yuri's Avatar
Rewards Points: 178
It probably has a short and is no good and unsafe. Go to HDepot and buy a good Honeywell Vision or Focus Pro type. Check the wires for abrasion, pinching. Go outside an check them at the A/C in case rodents chewed them or got hit by a weedwhacker. Try hang the wires in the air after labeling them at the tstat. Then one at a time jumper R-W see if furnace works, then R-Y see if A/C works, R-G see if fan works. If all is okay then the wires are good and it is the tstat. Get a new tstat anyway as yours are unsafe after all the shorting etc.
Old 10-04-2009, 05:08 PM   #28
Yuri, thanks for all your help. I finally traced it down to the white wire from the tstat. It must of been rubbing on somthing and it grounded out on the duct work somewhere. Forturnately I had an extra (blue) wire I was able to use. I certainly learned alot in the last two days, and while the original board probably wasn't bad (still not sure) it didn't hurt to have a new one for free. I'm just nervous now if and when the next wire will short out and where is the short?
Old 10-04-2009, 05:33 PM   #29
Hvac Pro
yuri's Avatar
Rewards Points: 178
That is why it is impossible to troubleshoot everything over the internet. LOL. Shorts are difficult to troubleshoot even for a Pro. Now you know as much as some Junior techs. If possible you may want to run a new 18/6 LVT wire to your tstat and then you have a extra C wire to it so the tstat can operate off the furnace power and save the batteries. Or relocate it to a different wall and run the wire thru a closet (another trick of the trade).
Good Luck and Pay it Forward (Help someone else).
Old 10-04-2009, 07:27 PM   #30
xxxxxxxxxx
Nordyne condenser goodman A-coil wtroger HVAC 10 09-16-2009 03:52 AM
Evaporator coil for Goodman A/C leschuler HVAC 2 09-25-2008 12:43 PM
goodman furnace nhicks HVAC 3 02-09-2008 06:25 PM
Replacing an 20 year old gas forced air with a 95% 2 stage goodman, goodman 40" tall, englewood1 HVAC 12 09-25-2007 11:37 PM
Sub is swapping Amana for Goodman Dragon HVAC 22 02-04-2007 07:54 AM