Goodman GMS90703BXA - HVAC - DIY Chatroom Home Improvement Forum
Old 10-02-2009, 06:00 PM   #1
Goodman GMS90703BXA
Switched thermostat to heat but nothing happened. The LED light is lit and when I shut power off to the machine the only thing I hear was a click...not fan, no ignitor..nothing.
The main blower motor works if I switch the fan to on from the thermostat.
Is this a ignitor problem?
ew&se is offline   Reply With Quote
Old 10-02-2009, 06:40 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,274
No. Do you own an electrical meter and know how to use it?
Old 10-03-2009, 12:00 AM   #3
Yes, I think I tested the ignitor correctly. I checked for connectivity with the meter set on OHM's. I believe the ignitor is good, but not sure. The furnace is only 5 years old.
Old 10-03-2009, 07:28 AM   #4
Hvac Pro
yuri's Avatar
Check for 24 volts between W and C on the circuit board with the tstat calling for heat. Door switch needs to be pressed in at the same time/put duct tape on it temporary. If no 24 volts your tstat may be faulty or a broken wire from it.
Old 10-03-2009, 01:06 PM   #5
No reading for AC or DC on W and C terminals
Old 10-03-2009, 01:10 PM   #6
Would it be ok if you called me or I called you? The local parts store closes at 4 today and really need to get this furnace working.
Old 10-03-2009, 01:13 PM   #7
Hvac Pro
yuri's Avatar
Sorry, I only help this way. If your LED is lit then you have power to the board and it means standby and OK. You should have 24 volts between R and C. If you do then jumper R and W at the tstat and see if it works. You may just need a new tstat.
Old 10-03-2009, 01:16 PM   #8
is there a quick way to bypass the tstat from the furnace to check if the tstat is bad
Old 10-03-2009, 01:19 PM   #9
Hvac Pro
yuri's Avatar
Jumper R and W at the board. I just finished looking at my neighbors unit/same as yours/lucky.
Old 10-03-2009, 01:25 PM   #10
when i jumped the R and W the LED went out and nothing happened
Old 10-03-2009, 01:32 PM   #11
Hvac Pro
yuri's Avatar
There should be a 3 amp fuse on the board which may have accidentally blown.
Old 10-03-2009, 01:37 PM   #12
I have 27 vac coming out of the transformer. I tried turning on the AC and that doesn't work either.
Old 10-03-2009, 01:38 PM   #13
Hvac Pro
yuri's Avatar
You still need to check for 24 volts from R to C as the fuse can be blown and transformer OK.
Old 10-03-2009, 01:43 PM   #14
The fuse is ok, the AC is actually working and it doesn't seem like the tstat isn't working.
Old 10-03-2009, 01:45 PM   #15
Hvac Pro
yuri's Avatar
If the LED is off then the board sounds bad. There should be a legend on the back of the doors with diagnostics and error codes, see if LED off means anything. It should be on and can flash a code if a press switch is open etc. If you jumpered R to W and you have 24 volts from R to C and no led it sounds like a bad board. The first thing that happens on a call for heat is the inducer fan starts.
Nordyne condenser goodman A-coil wtroger HVAC 10 09-16-2009 03:52 AM
Evaporator coil for Goodman A/C leschuler HVAC 2 09-25-2008 12:43 PM
goodman furnace nhicks HVAC 3 02-09-2008 06:25 PM
Replacing an 20 year old gas forced air with a 95% 2 stage goodman, goodman 40" tall, englewood1 HVAC 12 09-25-2007 11:37 PM