Goodman GMNT 080-4 Inducer Problem - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 03-25-2011, 08:07 PM   #16
An old Tradesmen
Rewards Points: 6,098
Sounds like a cracked heat exchanger. Turn the stat up so it runs, watch the flames, see if they change when the blower comes on.
Voltage is allowed to be plus or minus 10% of rated voltage. Rated at 115 volts, 104 to 126 is acceptable.
The Following User Says Thank You to beenthere For This Useful Post:
Doc Holliday (03-25-2011)
Old 03-26-2011, 12:58 AM   #17
AKA HVACTECHFW
Rewards Points: 1,208
if the crack were big enough to cause the inducer to fail, then the pressure switch would most likely catch that and not allow the unit to fire.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 03-26-2011, 03:37 AM   #18
how
Rewards Points: 1,070
It's a strange problem when the diagnostic's on the board are not giving you an indication of pressure drop that a failing inducer motor should give you
I would be looking for a connection or a line feed related to the inducer that is poor. Your voltage could be OK but an amp restriction due to a poor connection or a nearly severed line would explain the quick motor burnouts.
Oh and by the way... The company your tech worked for makes all the other heating companies in my area look good.
how is online now   Reply With Quote
Old 03-26-2011, 04:47 AM   #19
An old Tradesmen
Small cracks, or popped crimp rings often don't effect the pressure enough to keep the pressure switch from opening.
Recently replaced the inducer on a GUN, when the blower came on, the inducer changed noise. Middle cell was cracked. But the inducer was able to keep enough negative pressure that the switch stayed closed.
Doc Holliday (03-26-2011)
Goodman heating problem Eric4187 HVAC 2 03-08-2011 04:59 AM
Bryant Plus 90 398AAZ inducer motor PCWilson HVAC 10 02-27-2011 05:55 PM
Why is Inducer Fan Running? artbuc HVAC 3 07-31-2010 10:39 AM
Inducer motor or control circuit? Please help me troubleshoot. averagerob HVAC 1 03-03-2009 02:43 PM
Stymied by window leakage problem. Matth3w General DIY Discussions 5 06-11-2008 07:26 PM