Goodman Gas Furnace Cycling Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 02-15-2012, 05:47 PM   #1
Goodman gas furnace cycling problem
My Goodman furnace started multiple cycles off and on. I made sure all the vents were open and the filter was cleaned. I actually left it out and ran it that way for a few hours. It had no effect on the cycling. I removed the flame sensor and used a little steel wool on it. ReInstalled it left the access door off and tryed it again. It seems to not be cycling like it was it reach temperature
and shut off but if I put access door back on it starts up again. I would appreciate suggestion anyone has. Thanks ScottE
ScottE is offline   Reply With Quote
Old 02-15-2012, 06:05 PM   #2
how
Rewards Points: 1,104
Age /model or a picture of your Goodman with the doors off would help.
Do you have an led light flashing a diagnostic code on your board when the access door is back in place and your furnace is cycling on & off?
Most folks here are going to be wondering about if your vaccum switches are causing the cycling and why.
how is offline   Reply With Quote
Old 02-15-2012, 08:48 PM   #3
Goodman furnace recycling problem
Here is the rest of the story. It is a Goodman model GDH 80703axab
installed in 09/07. When the access door is in place and it's cycling off and on a lot it blinks 3 times for a while and then starts blinking 4 times. I also blew into the pressure switch and didn't hear anything but I sucked on it and heard it click. I also inspected the hose and it looks good. What do you think. ScottE
Old 02-15-2012, 09:07 PM   #4
Rewards Points: 582
is that furnace the one that is no longer available....seem to me I received a tech sheet from goodman... anyway sounds like combustion air restriction...
Old 02-15-2012, 09:13 PM   #5
GC/Master Plumber/Mech
Rewards Points: 560
Flash code 3 - Pressure switch
Flash code 4 - Open Limit
Is you filter dirty?
I think you need to work the FC 4 first since it lite up and works. If the pressure switch was your problem then the furnace would not fire.
Check the filter first
You said that removing the furnace door it runs fine and once the door is installed it starts acting up. Removing the door opens the return air and closing the door is telling me that the return is restricted.
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 02-15-2012, 09:23 PM   #6
Rewards Points: 582
AM i missing something here the door he removed is the access door to burnner and flame sensor compartment YES NO ..
Old 02-15-2012, 09:27 PM   #7
Rewards Points: 560
No Ben I'm Missing something Sorry mis read.
Although I think this OP may be miss counting the flash code. A code 3 & 4 never seen that before.
Maybe it a 3 code and by the OP "Blowing/Sucking" on the pressure switch the OP damaged the pressure switch.
The Following User Says Thank You to Plumber101 For This Useful Post:
ben's plumbing (02-15-2012)
Old 02-15-2012, 10:33 PM   #8
Goodman furnace cycling problem
Yes it is the door to the burner and flame sensor. better word would be panel not door. Did I mention the filter is clean. So what I'm hearing is if the burner is firing up then it is not the pressure switch, It is more likely the limit switch Thanks for your patience. I'm a out of work Carpenter, would rather call one of you guys to fix it. Thanks again for your help Scotte
Old 02-16-2012, 12:27 AM   #9
how
Hey Plumber 101 (Quote)
That's just not true.
I have often run into pressure switches causing a cycling of the burners. This can sometimes be a failing of the pressure switch or the inducer motor but what is common during testing is that the pressure created by the inducer is high enough to engage the pressure switch but a slow lowering of that pressure after a while has the burners cut out.
Today as an example I had an Airco 80% that measured 1.2 "WC tee'd between the ID and the pressure switch but would slowly reduce in pressure over 5 minutes below the switches .85 WC threashold. A seperate measurement of the ID assy alone confirmed the problem as the pressure switch.
The Following User Says Thank You to how For This Useful Post:
ben's plumbing (02-16-2012)
Aprilaire 700A on Goodman Furnace? kcrossley2 HVAC 50 02-18-2012 04:41 PM
Water Inside/Around American Standard Furnace michrob HVAC 8 12-08-2011 03:51 PM
Interminttent Ignition Problem Kero Furnace Chad22 HVAC 2 02-21-2011 08:04 AM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 01:45 AM
Goodman Furnace does not kick in wctoro HVAC 2 02-20-2008 01:47 PM