goodman furnace not lighting
I have a goodman gmp-100-4 100,000 btu furnaace that intermittantly wont light. Draft inducer comes on and i can hear pressur switch click then no further sequence and after a while the unit just shuts down. I did an experiment where i joined the 2 wires at he pressure switch and it ignighted. I am getting 3 blinks at the board which is PS code. Some times i can get it to light by jiggling wires around and other times i just give up after 20 minutes of messing with it. I used to get 4 blinks on board but that is now at 3 blinks...go figure. Now should i just get a PS and try it? OH and I do have air coming out of the exaust pipe when the draft inducer is on.
thanks
Bob M is offline   Reply With Quote
Old 02-29-2012, 10:19 AM   #2
how
Rewards Points: 1,104
If you hear a click in the ps when the ID comes on AND jumpering the ps completes the ignition cycle then you probably have a bad wire, wire connection or a faulty switch within the ps.
Just in case you are mistaken about hearing the click from the ps, I would make sure the ps tube to the inducer is clear & dry, firmly snugged in place without any end splits, and I'd also be poking a paperclip into the ID port to make there is no build up of crud there.
how is offline   Reply With Quote
Old 02-29-2012, 04:04 PM   #3
An old Tradesmen
Rewards Points: 7,380
GMP. Probably has a cracked heat exchanger, or popped crimp rings.
The Following User Says Thank You to beenthere For This Useful Post:
ben's plumbing (02-29-2012)
Old 02-29-2012, 08:09 PM   #4
HVAC Tech/ Browns Fan
Check the round switch's that had little pop button. Push it in if popped out. Restart it and if works then shut it off!! That is sign of roll out ( crack heat exchanger)
Tator1076 is offline   Reply With Quote
Old 02-29-2012, 08:16 PM   #5
Rewards Points: 582
found 5 units this winter with bad heat exchangers.....not a good sign..
Old 02-29-2012, 08:28 PM   #6
I did one last week and it had 23 cracks.
Aprilaire 700A on Goodman Furnace? kcrossley2 HVAC 50 02-18-2012 04:41 PM
Help Needed. Goodman furnace jzw HVAC 14 01-01-2011 11:21 PM
Goodman gas furnace electronic ignitor rperry HVAC 4 02-10-2010 04:39 PM
Goodman Gas furnace, A/C will not run new install RCApp HVAC 5 08-04-2009 09:00 PM
Gas furnace not lighting, but damper moves tevans HVAC 5 11-15-2006 09:01 PM