Old 05-04-2012, 11:52 AM   #1
Question
Goodman A24-05 Evap motor
Hello all,
I have a Goodman A24-05. The Evaporator motor stops running or will not come on I am not sure what happens but the compressor will run and stay running. Since the blower motor is not running air threw the evaporator it freezes. I can take the lead off the BTDR or time delay relay and manually make the connection to the #3 terminal this starts the fan. I can put is back to the #1 terminal wait a few seconds and it starts up and starts pulling air. There is no set time when this happens it could be in the afternoon or it could be in the evening. The only way we notice it that the a/c stops cooling the house. Any Ideas? The coils are clean, and new filter.
jrbb is offline   Reply With Quote
Old 05-04-2012, 11:54 AM   #2
I'm Your Huckleberry
Control board, stat, motor run capacitor or motor. Could be any one of those things when a motor sometimes comes on and sometimes does not.
I'd start with the run cap first.
Thanks.
Doc Holliday is offline   Reply With Quote
The Following User Says Thank You to Doc Holliday For This Useful Post:
jrbb (05-04-2012)
Old 05-04-2012, 12:00 PM   #3
Question
DOC what is a STAT. By control board do you mean the thermostat? I cannot find a control board in the schematics anywhere. Thank for your replay
Old 05-04-2012, 12:01 PM   #4
Old 05-04-2012, 12:03 PM   #5
Thermostat, the thing on your wall that you switch onto fan, cool or heat that brings on or turns off the system.
Thanks.
Old 05-04-2012, 12:05 PM   #6
kilosos2's Avatar
delete
kilosos2 is offline   Reply With Quote
Old 05-04-2012, 12:07 PM   #7
I have a spare cap I will give it a whorl.
Old 05-04-2012, 12:50 PM   #8
Don't go putting in any old capacitor. Check the size by way of number of the one that's on the motor and put in the exact same mfd cap.
Thanks.
Old 05-04-2012, 01:08 PM   #9
Originally Posted by kilosos2 View Post
delete
I probably should've been more specific, many people don't understand our hvac slang.
Thanks.
Old 05-04-2012, 01:13 PM   #10
kilosos2's Avatar
loll
I typed something to reply to the OP but I saw you already answered him so I deleted it. loll
Let's light the fire and burn the tires!
Old 05-04-2012, 01:15 PM   #11
loll
Thanks.
Old 06-01-2012, 04:58 PM   #12
I installed a new capacitor and that fix the not coming on problem. It seemed to run allot better as well. I also disconnected and isolated the leads to the heat coil and that made a world of difference. It cools the house far better I just need to see why the heater coils would come on when the A/C comes on. Wish me luck!
Old 06-01-2012, 06:03 PM   #13
kilosos2's Avatar
Heater ON when you call for cooling? Did you recently install a thermostat? Well before you had your problem? It maybe wired wrong. OR the Heater Relay maybe messed up some how and is being energized as cooling is being energized also. (weird don't know how that happens, unless someone from beginning wired the unit WRONG)
Tags
a2405, air handler, goodman
How to replace condensor fan motor? twags HVAC 41 09-13-2012 07:05 PM
Goodman motor availability NomadTrash HVAC 5 11-08-2008 12:01 PM
Replacing a Condenser Fan Motor (Goodman) guddug HVAC 8 07-03-2008 11:11 PM
Replacing a Condenser Fan Motor thothtp HVAC 5 06-08-2008 07:30 PM
new evap fan motor wont work blansie Appliances 1 05-13-2008 12:43 AM