Goodman 80%, Igniter Glows No Flame - HVAC - DIY Chatroom Home Improvement Forum
Old 10-31-2008, 10:44 PM   #1
Goodman 80%, igniter glows no flame
Hello, Please help... I have reviewed a lot of the posts looking for this same problem but none seem to be exactly the problem I am having... I have a Goodman 80%, 10-15 yrs old... The vent blower runs for about 15 seconds and then I hear a clicking sound and eventually notice the igniter starting to glow and then all shuts down... The combined time from the clicking sound to shutdown is about 7-10 secs... I never hear any sound from the gas valve (solenoid clicking) indicating it is being activated... Is the igniter supposed to be ON for a set amount of time before shutting down??? It doesn't seem to be ON long enough to ignite the burner but then again as I mentioned I don't think the gas valve is opening...
I have removed the flue pipe to eliminate the question of blockage and I have checked the flow switch which I think if it wasn't working the igniter wouldn't glow at all... I took the hose off the vent blower and sucked on the end and get the same operation... Thank you for any input you can give... John
diyjohn is offline   Reply With Quote
Old 11-01-2008, 02:20 AM   #2
HvacWiz's Avatar
Rewards Points: 252
You will need a meter to check if you are getting 24v at the gas valve.
HvacWiz is offline   Reply With Quote
Old 11-01-2008, 11:51 AM   #3
Thank you HvacWiz... I am picking up a volt meter today from my son... mine has a blown fuse... if it is determined to have current at the valve then I would assume the solenoid is faulty and should be replaced... are they replaceable??? However if no current at the valve what would be the next item to check??? Enjoy the Day, John
Old 11-01-2008, 12:24 PM   #4
Hey Diyjohn!
When it comes time to give the the meter back, do like our kids do when we loan them a tool: "I don't remember no meter".
I'm still trying to get my American made Dewalt circular saw back from my Pecker Head son.
Damn kids
hvaclover is offline   Reply With Quote
Old 11-03-2008, 02:57 AM   #5
Hello HvacWiz, i did test for voltage at the gas valve.... Nothing there so i proceeded to the transformer and had 115v on one side and nothing on the other... I assume this means the transformer is defective??? You know i did have th furnace running a cpl weeks ago with no problem... I guess a transformer can just quit working all together... Thank you, John
Old 11-03-2008, 06:36 AM   #6
An old Tradesmen
Rewards Points: 8,242
If the transformer was bad.
The board wouldn't be able to run the inducer or ignitor when the stat calls.
The board needs 24 volts to do anything.
Old 11-03-2008, 01:35 PM   #7
Thank you... the transformer has 2 connectors on the bottom side and i had a reading of 115v and there were 2 connectors at the top which i had no reading at all... One of the two top connectors has a double connector (piggyback) of which one wire runs to the metal housing as a ground and the other to the circuit board... Am i checking this properly??? Yes the igniter glows and the vent blower is operating...
Old 11-03-2008, 03:37 PM   #8
Your transformer is fine...the problem is either a bad gas valve or a bad board. What is the model # of your furnace?
AccuAir is offline   Reply With Quote
Old 11-03-2008, 04:33 PM   #9
An old Tradesmen
You must be.
If it was bad, the board wouldn't be able to run the inducer or ignitor.
Old 11-03-2008, 05:04 PM   #10
Been is right if you are giving an accurate estimate of the furnace age.
Some how you are missing the 24 v supply.
Old 11-03-2008, 09:00 PM   #11
The problem is that the ignitor is not pulling enough amps to open valve to allow gas to flow. Replace glowbar and it will work, if it don't pull the required amps that is around 3.2 amp draw to open valve, check it with clamp on meter. They will glow all day long without lighting. I was a service technician for Amerigas for quite a while.
simpleman1962 is offline   Reply With Quote
Old 11-03-2008, 09:20 PM   #12
You should remove one the secondary wire connections and check for the 24 volts.
You should read the 24 volts. If not the transformer is bad.
If you have 24 volts and it goes to nothing with the wires connected, it means that there is a short circuited load!
Old 11-03-2008, 09:23 PM   #13
I am willing to bet that the ignitor is bad believe what you want.
Old 11-03-2008, 09:53 PM   #14
In the original post he said that the igniter was glowing!
This tells me that something else is happening! You could very well be right, as you obviously have had experience with these!
Old 11-03-2008, 10:59 PM   #15
Amperage on the HSI does not open the valve. If the HSI is weak then the warm up won't be hot enough. The gas valve will still open but if no flame is sensed in .08 seconds it will retry until lock out. The inducer motor would purge what little gas there was released.
You got a meter, so wait for the igniter to cool to room temp and ohm it out.
Goodman Furnace GMNT100-4b Won't stay on freeslporer HVAC 3 10-30-2008 06:42 PM
Flame blowin' in the wind... testeng HVAC 4 10-28-2007 03:11 PM
Sub is swapping Amana for Goodman Dragon HVAC 22 02-04-2007 07:54 AM
Trouble - Goodman GMP100-3 Rev B cstelter HVAC 1 10-24-2006 12:27 PM